[RE-wrenches] New Outback FXR Series as GTGBB on existing Off Grid Home
Bradley Bassett
bbassett2 at gmail.com
Thu Oct 24 16:55:12 PDT 2024
As I remember the FXR inverters will rarely connect to any generators
beside very well controlled or inverter type generators. I agree that I
don't think there is any automatic transfer from grid tie to generator
input.
Brad Bassett
On Thu, Oct 24, 2024 at 3:42 PM Wayne Irwin via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> It is my understanding that the FXR will not "automatically" switch from
> Grid Input to Gen.
> To my knowledge this is a manual option only.
> I do not recall any way to make this happen automatically. That would have
> been great.
>
> You can however still call for the generator at a low V setting and have
> the generator power an external charger to boost the batteries.
> I think the brand we used to use was IOTA however, I have also seen golf
> cart chargers used.
>
>
> Wayne Irwin
> President
> License #CVC56695
> State Licensed Solar Contractor
> Pure Energy Solar International Inc.
> Wayne at PureEnergySolar.com
> PureEnergySolar.com <http://pureenergysolar.com/>
> SolarChargingStation.com <http://solarchargingstation.com/>
> 352 377-6527 Office
> 352 336-3299 Fax
>
>
> The Sun Is Always Shining!
>
> The content of this message is Pure Energy Solar Confidential. If you are
> not the intended recipient and have received this message in error, any use
> or distribution is prohibited. Please notify me immediately by reply e-mail
> and delete this message from your computer system. Thank you.
>
> ------------------------------
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> on behalf
> of Jay via RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Sent:* Thursday, October 24, 2024 5:57 PM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Cc:* Jay <jay.peltz at gmail.com>
> *Subject:* Re: [RE-wrenches] New Outback FXR Series as GTGBB on existing
> Off Grid Home
>
> Hi Jeremy
>
> There are two issues I think.
>
> 1 is that the inverter won’t connect.
> And I don’t have an answer why the inverter won’t in sell mode but will in
> gen mode. Maybe the generator is slightly out of the more narrow window for
> grid. I presume you’ve checked hz and volts and they are in spec for grid?
> I know sometimes the frequency control can be slightly variable without a
> load. I’ve had success in the past getting inverters to connect to a
> generator with putting some dumb loads on it. Like incandescent lights or
> small heater.
>
> 2. Maybe it’s a good thing it won’t because if it did connect wouldn’t it
> be possible for the inverter to try to sell to the generator? If you
> didn’t have to change grid to Gen?
>
> Jay
>
> On Oct 23, 2024, at 8:47 PM, Jeremy Rodriguez via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>
> Wrenches,
> We have a client that has brought utility power in and we now have the
> system hooked up to the utility.
> In setting the system up, I've experienced that the inverter will sell and
> function fine with all the settings set up as* Grid Tied* mode, but it
> does not play nice when the grid is gone , and the Generator is brought in
> as the AC source.
> We have installed an external transfer switch to switch the inverters' AC
> input, from either the utility or the existing backup generator ( if the
> grid fails), automatically.
>
> The manual states that the inverter's two input selections can be
> programmed for seperate input modes, via the* Input* *Type* menu. Ive not
> been able to get this accomplished.
>
> When simulating a grid outage, thus changing the AC input to the inverter
> being from the Generator, the inverter will not synch to the AC power to
> charge the batteries.
> The only way that I can get the inverter to synch, is to switch the input
> mode to *GEN* from *GRID.*
> This is not ideal since the client would need to be present to make the
> button push, even though the generator will be started automatically if the
> grid were to go down (hopefully) , just as it did before.
>
> With no way to contact Outback , can someone advise how to properly
> program the inverter/ MATE3S for this project?
> Equipment onsite:
> Single VFXR3648 inverter
> Two FM60 CCs
> Hub4
> MATE3S
> ATS with Dual Relays 50A
> L.A. Battery bank
>
> Here's how we would like it to work:
> Utility power ON:
> Sell excess power once the batteries have gone through the Absorb cycle.
> Batteries remain full in case of a utility failure.
> Utility Outage:
> ATS now feeds Inv AC input via Generator if needed.
> Inverter runs the home as it did , off grid.
> If the battery voltage drops and the AGS is engaged, the inverter will use
> that input to charge the batteries as usual. If the grid comes back on and
> the gen is running, the generator can still run, with no connection to the
> inverter. With the grid now charging the battery bank, and the AGS will
> enventually shut off the Gen. Based on voltage.
> Contact me off list if necessary
>
>
> Jeremy Rodriguez
> All Solar Inc.
> Penrose, CO
> 719-276-4954
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20241024/6dd02eea/attachment.htm>
More information about the RE-wrenches
mailing list