<div dir="ltr">As I remember the FXR inverters will rarely connect to any generators beside very well controlled or inverter type generators. I agree that I don't think there is any automatic transfer from grid tie to generator input. <div><br></div><div>Brad Bassett</div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Thu, Oct 24, 2024 at 3:42 PM Wayne Irwin via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><div class="msg-3789175476620558">




<div dir="ltr">
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
It is my understanding that the FXR will not "automatically" switch from Grid Input to Gen. </div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
To my knowledge this is a manual option only.</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
I do not recall any way to make this happen automatically. That would have been great.</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
<br>
</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
You can however still call for the generator at a low V setting and have the generator power an external charger to boost the batteries.</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
I think the brand we used to use was IOTA however, I have also seen golf cart chargers used.</div>
<div id="m_-3789175476620558Signature">
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
<br>
</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
<br>
</div>
<div style="direction:ltr;font-size:12pt"><span style="font-family:calibri,helvetica,sans-serif;color:rgb(6,64,12);background-color:rgba(0,0,0,0);line-height:normal">Wayne Irwin</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(0,0,0)"><br>
</span><span style="font-family:calibri,helvetica,sans-serif;color:rgb(6,64,12);background-color:rgba(0,0,0,0);line-height:normal">President</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(0,0,0)"><br>
</span><span style="font-family:calibri,helvetica,sans-serif;color:rgb(6,64,12);background-color:rgba(0,0,0,0);line-height:normal">License #CVC56695</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(0,0,0)"><br>
</span><span style="font-family:calibri,helvetica,sans-serif;color:rgb(6,64,12);background-color:rgba(0,0,0,0);line-height:normal">State Licensed Solar Contractor</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(0,0,0)"><br>
</span><span style="font-family:calibri,helvetica,sans-serif;color:rgb(6,64,12);background-color:rgba(0,0,0,0);line-height:normal">Pure Energy Solar</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(6,64,12)"> International
 Inc.</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(0,0,0)"><br>
</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(6,64,12)">Wayne@PureEnergySolar.com</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(0,0,0)"><br>
<a href="http://pureenergysolar.com/" id="m_-3789175476620558OWAa4ceda25-a3ff-8b02-b862-900cab607a20" title="http://pureenergysolar.com/" target="_blank">PureEnergySolar.com</a><br>
<a href="http://solarchargingstation.com/" id="m_-3789175476620558OWAfe3fc7bc-55b4-9327-c302-d057a7412077" title="http://solarchargingstation.com/" target="_blank">SolarChargingStation.com</a><br>
</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(6,64,12)">352 377-6527 Office</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(0,0,0)"><br>
</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(6,64,12)">352 336-3299 Fax</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(0,0,0)"><br>
<br>
<br>
</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(6,64,12)">The Sun Is Always Shining!</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(0,0,0)"><br>
<br>
The content of this message is Pure Energy Solar Confidential. If you are not the intended recipient and have received this message in error, any use or distribution is prohibited. Please notify me immediately by reply e-mail and delete this message from your
 computer system. Thank you.</span></div>
<div style="direction:ltr;font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
<br>
</div>
</div>
<div id="m_-3789175476620558appendonsend"></div>
<hr style="display:inline-block;width:98%">
<div id="m_-3789175476620558divRplyFwdMsg" dir="ltr"><font face="Calibri, sans-serif" style="font-size:11pt" color="#000000"><b>From:</b> RE-wrenches <<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>> on behalf of Jay via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>><br>
<b>Sent:</b> Thursday, October 24, 2024 5:57 PM<br>
<b>To:</b> RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>><br>
<b>Cc:</b> Jay <<a href="mailto:jay.peltz@gmail.com" target="_blank">jay.peltz@gmail.com</a>><br>
<b>Subject:</b> Re: [RE-wrenches] New Outback FXR Series as GTGBB on existing Off Grid Home</font>
<div> </div>
</div>
<div dir="auto">
<div dir="ltr"></div>
<div dir="ltr">Hi Jeremy</div>
<div dir="ltr"><br>
</div>
<div dir="ltr">There are two issues I think. </div>
<div dir="ltr"><br>
</div>
<div dir="ltr">1 is that the inverter won’t connect. </div>
<div dir="ltr">And I don’t have an answer why the inverter won’t in sell mode but will in gen mode. Maybe the generator is slightly out of the more narrow window for grid. I presume you’ve checked hz and volts and they are in spec for grid?  I know sometimes
 the frequency control can be slightly variable without a load. I’ve had success in the past getting inverters to connect to a generator with putting some dumb loads on it. Like incandescent lights or small heater. </div>
<div dir="ltr"><br>
</div>
<div dir="ltr">2. Maybe it’s a good thing it won’t because if it did connect wouldn’t it be possible for the inverter to try to sell to the generator?  If you didn’t have to change grid to Gen?</div>
<div dir="ltr"><br>
</div>
<div dir="ltr">Jay</div>
<div dir="ltr"><br>
<blockquote type="cite">On Oct 23, 2024, at 8:47 PM, Jeremy Rodriguez via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>> wrote:<br>
<br>
</blockquote>
</div>
<blockquote type="cite">
<div dir="ltr">
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
Wrenches, </div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
We have a client that has brought utility power in and we now have the system hooked up to the utility.</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
In setting the system up, I've experienced that the inverter will sell and function fine with all the settings set up as<b> Grid Tied</b> mode, but it does not play nice when the grid is gone , and the Generator is brought in as the AC source.</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
We have installed an external transfer switch to switch the inverters' AC input, from either the utility or the existing backup generator ( if the grid fails), automatically. </div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
<br>
</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
The manual states that the inverter's two input selections can be programmed for seperate input modes, via the<b> Input</b>
<b>Type</b> menu. Ive not been able to get this accomplished. </div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
<br>
</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
When simulating a grid outage, thus changing the AC input to the inverter being from the Generator, the inverter will not synch to the AC power to charge the batteries. </div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
The only way that I can get the inverter to synch, is to switch the input mode to
<b>GEN</b> from <b>GRID.</b></div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
This is not ideal since the client would need to be present to make the button push, even though the generator will be started automatically if the grid were to go down (hopefully) , just as it did before.</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
 </div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
With no way to contact Outback , can someone advise how to properly program the inverter/ MATE3S for this project?   </div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
Equipment onsite:</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
Single VFXR3648 inverter</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
Two FM60 CCs</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
Hub4</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
MATE3S</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
ATS with Dual Relays 50A </div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
L.A. Battery bank</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
<br>
</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
Here's how we would like it to work:</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
Utility power ON: </div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
Sell excess power once the batteries have gone through the Absorb cycle. Batteries remain full in case of a utility failure. </div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
Utility Outage: </div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
ATS now feeds Inv AC input via Generator if needed.</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
Inverter runs the home as it did , off grid.</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
If the battery voltage drops and the AGS is engaged, the inverter will use that input to charge the batteries as usual.  If the grid comes back on and the gen is running, the generator can still run, with no connection to the inverter.  With the grid now charging
 the battery bank, and the AGS will enventually shut off the Gen. Based on voltage.  </div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
Contact me off list if necessary</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
<br>
</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
<br>
</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
Jeremy Rodriguez</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
All Solar Inc. </div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
Penrose, CO</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
719-276-4954</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
<br>
</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
<br>
</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
<br>
</div>
<span>_______________________________________________</span><br>
<span>List sponsored by Redwood Alliance</span><br>
<span></span><br>
<span>Pay optional member dues here: <a href="http://re-wrenches.org" target="_blank">http://re-wrenches.org</a></span><br>
<span></span><br>
<span>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a></span><br>
<span></span><br>
<span>Change listserver email address & settings:</span><br>
<span><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></span><br>
<span></span><br>
<span>There are two list archives for searching. When one doesn't work, try the other:</span><br>
<span><a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a></span><br>
<span><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a></span><br>
<span></span><br>
<span>List rules & etiquette:</span><br>
<span><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">http://www.re-wrenches.org/etiquette.htm</a></span><br>
<span></span><br>
<span>Check out or update participant bios:</span><br>
<span><a href="http://www.members.re-wrenches.org" target="_blank">http://www.members.re-wrenches.org</a></span><br>
<span></span><br>
</div>
</blockquote>
</div>
</div>

_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</div></blockquote></div>