[RE-wrenches] Sol-Ark 15KW is rock steady, but crazy wild grid voltages when connected to grid

drake.chamberlin at redwoodalliance.org drake.chamberlin at redwoodalliance.org
Fri Sep 13 03:33:32 PDT 2024



Check for voltage fluctuation at the main lugs, right where the service 
cable comes in from the meter.

---

_Drake Chamberlin_

_Athens Electric LLC_

_Ohio Electrical Contractor's License 44810_

_NABCEP Certified PV Installation Professional_

On 2024-09-12 21:54, Kirpal Khalsa via RE-wrenches wrote:

> Scot,
> We have had numerous SolArk 15k's with loose neutrals direct from the 
> factory.   Double check all the factory connections in the accessible 
> wiring compartment.  I brought it to their attention each time I found 
> it. They said they would do better on quality control bit obviously 
> never heard back after that.
> Keep us posted what you find.
> Thanks
> 
> Kirpal Khalsa
> Oregon Solarworks
> 
> On Thu, Sep 12, 2024, 6:41 PM Blake Gleason via RE-wrenches 
> <re-wrenches at lists.re-wrenches.org> wrote:
> 
> Definitely sounds like a loose neutral on the utility side (likely at 
> the pole/tap).
> 
> I suspect if you turn off and disconnect the Sol-Ark the light 
> flickering, etc will continue (until the utility recrimps their 
> neutral...)
> 
> Blake
> 
> On Thu, Sep 12, 2024 at 5:38 PM Scot Arey via RE-wrenches 
> <re-wrenches at lists.re-wrenches.org> wrote:
> 
> I have Sol-Ark 15KW with 31kwh battery has been installed for year+.
> 
> Customer has for two days been having grid voltage issue seen as 
> dimming lights. No neighbors reporting issues. He called his 
> electrician who noted one high conductor and the other low. Have seen 
> this before unrelated to solar and it was a bad neutral. His 
> electrician says ok.
> 
> Customer disconnects from the grid because the fluctuations so severe 
> and when he does, voltage issues go away and Sol-Ark is rock steady at 
> 120-volts per leg. I send my senior tech over to ensure we don't have a 
> loose neutral or any grid conductors to the grid input. Nothing found.
> 
> Picture attached of grid voltages from the Sol-Ark monitoring (very 
> helpful, I might add.)
> 
> The electric cooperative is sending a tech out tomorrow. Any body have 
> insight or history with this?
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try 
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
> --
> 
> Blake Gleason, PE | Employee Owner
> Director of Innovation and Technical Excellence
> O: 510-845-2997 x128
> C: 510-867-5878
> 
> [1]
> 
> [2]
> 
> 1035 Folger Ave. [3]
> Berkeley, CA 94710 [3]
> www.sunlightandpower.com [1]
> License #326203
> 
> [4]  [5]  [6]  _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try 
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Links:
------
[1] http://www.sunlightandpower.com/
[2] https://linktr.ee/SLP_Socials
[3] 
https://www.google.com/maps/search/1035+Folger+Ave.+Berkeley,+CA+94710?entry=gmail&source=g
[4] https://benefitcorporationsforgood.com/
[5] https://www.amicussolar.com/
[6] https://calssa.org/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240913/5cac1f0c/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 136365 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240913/5cac1f0c/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: blocked.gif
Type: image/gif
Size: 118 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240913/5cac1f0c/attachment.gif>


More information about the RE-wrenches mailing list