[RE-wrenches] Sol-Ark 15KW is rock steady, but crazy wild grid voltages when connected to grid

pgiroux at mindspring.com pgiroux at mindspring.com
Fri Sep 13 04:33:47 PDT 2024


Scot

 

  We had this exact same thing happen last year with a 15. Voltage swings
got pretty wild. It was a bad neutral in the meter base. Older meter base
that had leaked and the neutral was a bar that compressed against the back
of the base. Corroded and gunked up from the years of that small leak,
needed a new meter base.

 

Peter Giroux

American Solar

 

From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of
Scot Arey via RE-wrenches
Sent: Thursday, September 12, 2024 8:37 PM
To: 'RE-wrenches' <re-wrenches at lists.re-wrenches.org>
Cc: scot.arey at solarcentex.com
Subject: [RE-wrenches] Sol-Ark 15KW is rock steady, but crazy wild grid
voltages when connected to grid

 

I have Sol-Ark 15KW with 31kwh battery has been installed for year+.

 

Customer has for two days been having grid voltage issue seen as dimming
lights. No neighbors reporting issues. He called his electrician who noted
one high conductor and the other low. Have seen this before unrelated to
solar and it was a bad neutral. His electrician says ok.

Customer disconnects from the grid because the fluctuations so severe and
when he does, voltage issues go away and Sol-Ark is rock steady at 120-volts
per leg. I send my senior tech over to ensure we don't have a loose neutral
or any grid conductors to the grid input. Nothing found.

Picture attached of grid voltages from the Sol-Ark monitoring (very helpful,
I might add.)

The electric cooperative is sending a tech out tomorrow. Any body have
insight or history with this?

 

 



 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240913/06584c2c/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 136365 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240913/06584c2c/attachment-0001.png>


More information about the RE-wrenches mailing list