[RE-wrenches] Schneider Rapid shutdown with 2023 compliance
Dave Angelini Offgrid Solar
offgridsolar at sti.net
Tue Jan 2 11:26:36 PST 2024
You said that very nicely Kevin !
If this were for offgrid, I would make the inspector happy and do even
more than Kevin suggests after he is gone. 😉
Link to RS shutdown
https://www.youtube.com/watch?v=wMoVXq4m1wk&t=10s
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[1]https://offgridsolar1.com/ [2] [1]
e-mail offgridsolar at sti.net
text 209 813 0060
On 2024-01-02 10:24 am, Kevin Pegg via RE-wrenches wrote:
> Hi Mac,
>
> I've just gone through a couple installations with a similar situation.
>
> The hardware you list does work as intended. I had to go through three
> different suppliers to get all the components.
>
> One thing that I didn't find clear in the MPPT RS documentation is when
> a shutdown is initiated, it shuts __everything__ on the Xanbus network
> down. All devices go into standby mode. Gen shuts down if running.
> Power is off. Not just the PV via Tigo modules. Had to develop client
> instruction sheet as to how to power up after a shutdown.
>
> On one hand, I can see why a single point shutdown is desired outcome.
> But it concerns me that it's vulnerable to abuse. If the whole system
> shutdown is not desired, the Xanbus connection can be omitted and then
> RS will be limited to the PV modules only.
>
> Kevin
>
> From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf
> Of Mac Lewis via RE-wrenches
> Sent: January-01-24 12:00 PM
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Cc: Mac Lewis <maclewis1 at gmail.com>
> Subject: [RE-wrenches] Schneider Rapid shutdown with 2023 compliance
>
> Hello Wrenches,
>
> I need to retrofit a Schneider XW+ system with a rapid shutdown system.
> The owner purchased this equipment about 4-5 years ago but is trying
> to get it past a very intense inspector.
>
> To me, it looks relatively straightforward to get NEC 2023 rapid
> shutdown compliant using Tigo TS4AF, and adding Schneider's MPPT
> Disconnect RS and external rapid shutdown initiator. It's a little
> strange though because it has 2017 NEC compliant all over the
> documentation but I believe we are good through NEC 2023 because
> shutdown occurs at a module level and the Disconnect RS can take care
> of arc-fault monitoring.
>
> Does anyone have any documentation for the MPPT Disconnect RS that
> doesn't specifically call out (only) NEC 2017 compliant?
>
> Or if this is not a good approach and is not reliable, I would
> appreciate your input as well.
>
> Cheers!
>
> --
>
> Mac Lewis
>
> "Yo solo sé que no sé nada." -Sócrates
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
Links:
------
[1] http://members.sti.net/offgridsolar/
[2] https://offgridsolar1.com/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240102/61cce944/attachment.htm>
More information about the RE-wrenches
mailing list