[RE-wrenches] Radian Question
Jay
jay.peltz at gmail.com
Sun Oct 29 12:45:02 PDT 2023
Hi drake
The early mate 3 has a glitch which I think they changed in the 3s.
You e got to set the rebulk volts above what you want it to charge at.
IE if the battery volts don’t get below the rebulk volts it won’t charge.
So if your shallow cycling the batteries it’s common it won’t get below the rebulk volts. If you’re deep cycling it usually will with default settings
The default high voltage window for ac input is default at 140v.
Hope this helps
Jay
> On Oct 29, 2023, at 11:14 AM, Drake Chamberlin via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>
>
> My Radian GS 8048 intermittently will connect to the grid to charge batteries. The grid voltage seems to run high around here. Yesterday, it wouldn't connect. The grid voltage was at 251 V. Later it did connect. At that point the grid was at 246 V.
>
> I am suspecting that the Radian has a voltage acceptance limit of 250 V. Is that true? Is it possible to open up the window?
>
> If that isn't it, what could be the problem?
>
> Thank you,
>
> Drake
>
> Drake Chamberlin
>
> Athens Electric LLC
>
> Ohio Electrical Contractor’s License 44810
>
> NABCEP Certified PV Installation Professional
>
>
>
>
> --
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20231029/24d1ad8a/attachment.htm>
More information about the RE-wrenches
mailing list