[RE-wrenches] Lithium battery charge rate
Starlight
larry at starlightsolar.com
Wed Jun 28 08:46:22 PDT 2023
That makes more sense, Darryl, thanks for sharing that. Another good example, Jay.
We do have batteries that can be charged at 3C but I have only designed one mobile medical unit with that capability. It required 2 50A shore power connections or could use the onboard 20kW generator. Makes lots of heat doing so and heat is battery enemy #1, molten salt batteries excluded. Lower operating temperatures is a good reason for using lower C rates.
Larry Crutcher
Starlight Solar Power Systems
On Jun 27, 2023, at 7:49 PM, Darryl Thayer via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
Hi Jay and all, I belive Steve meant C/2 or C/3; just a typo. My oldest set of LiFe is almost 10 years? It has a fastest charge rate of C/0.2 because the 10 kWh is charged by 1.6 kW solar. These batteries are doing fine. I do not have a way of measuring the current capacity but
On Mon, Jun 26, 2023 at 3:58 PM Jay via RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org>> wrote:
Hi All
I’m wondering if minimum charge amps for lithium is common or not?
Or does it have to do with the cell shape: cylindrical vs prismatic vs pouch?
A client purchased some EG4 batteries and they are getting a bit out of balanced. Tech support didn’t suggest higher volts or longer absorb but did mention they need 30-50 amps charge. It’s not in the manual.
Wondering what you all think and know
Thx
Jay
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20230628/14526b6b/attachment.htm>
More information about the RE-wrenches
mailing list