[RE-wrenches] Schneider SCP / MPPT 80 600 / XW+ / Gateway questions

Jay jay.peltz at gmail.com
Sun Jun 11 10:49:58 PDT 2023


Hi greg

There was just a thread that discussed you can’t use the scp to program the pro. Have to use insight. 
If I understand correctly. 

Hopefully others more knowledgeable will chime in about your other issues too. 

Good luck

Jay


> On Jun 11, 2023, at 11:37 AM, greg egan via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
> 
>  Friends, 
> 
> I'm currently onsite with a system.  Just replaced 4 XW + 6848's with 4 XW Pros.  Updated the Gateway to rev. 1.17 and the Pros to 2.04.  Have some questions/observations so far.
> 
> System: Off Grid with 4 XW Pros, 18 MPPT 80 600s, 2 SCPs, 1 Gateway, 1 Battery Monitor, 1 AGS.  3000 ahr of NiFe batteries.  36 kW Kubota Genset.
> 
> I tried using the Inverter SCP to program settings on the new inverters and it took everything but when I checked on InsightLocal the settings had not changed.  They were all still default so I had to go through it again one at a time through insightlocal.  I'm guessing the SCP no longer works for programming with the Gateway?  Can anyone confirm?  Programming used to work through the SCP with the old XW+ inverters and firmware.  
> 
> Tried using the Solar SCP to change settings on the charge controls but had to use insight local to change each individually.  Used to be able to use  the "copy from" function which was a real time saver.  Wondering if anyone else has run into the same problem, or if it works for them, what am I missing?  Is there a cool way to change one setting with insightlocal and get it to change the other 17?  
> 
> Observations:
> - looking at the CC's via insightlocal,
>     under configuration -> advanced ->controls - I set all chargers "enabled" but the next day or so they all go to "disabled".  They all still work though.  Doesn't seem to affect operations.  
> 
>     under configuration -> advanced ->charger settings - I have the first CC set to "primary" and the rest to secondary.  No idea if that's right or not.  seems to work.  Options are "stand-alone, primary, secondary and echo".  I could not find definitions in the manual on them.  
> 
> - looking at the XW Pros via insight local,
>     under configuration -> advanced ->controls -> Backup Mode - I disabled BAckup mode since I'm not backing up the grid. System shut down immediately.  Backup mode must be enabled when you're off grid.  
> 
> Thanks in advance : )
> 
> Greg Egan
> Remote Power Inc
> Fairbanks, AK
> 
> 
>      
> 
> 
> 
> 
> 
> 
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20230611/4003604d/attachment.htm>


More information about the RE-wrenches mailing list