[RE-wrenches] Schneider SCP / MPPT 80 600 / XW+ / Gateway questions

Dave Angelini Offgrid Solar offgridsolar at sti.net
Sun Jun 11 11:15:28 PDT 2023


It is pretty well laid out on the website for 3 + years that you need to 
use Insight.
You should also read the installer info.

https://solar.se.com/us/en/2021/06/29/essential-advanced-resources-for-installers/

SCP will work for some basic functions but is out of memory for XWP. Use 
for indication only.

I am guessing that you did not program XWP to set the IEE region code as 
above in the installers manual?  This is probably causing some extra 
issues for you.

You do need the password and I can send it if you do not have it?

Good Luck.

Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  offgridsolar at sti.net
text 209 813 0060

On 2023-06-11 10:37 am, greg egan via RE-wrenches wrote:

> Friends,
> 
> I'm currently onsite with a system.  Just replaced 4 XW + 6848's with 4 
> XW Pros.  Updated the Gateway to rev. 1.17 and the Pros to 2.04.  Have 
> some questions/observations so far.
> 
> System: Off Grid with 4 XW Pros, 18 MPPT 80 600s, 2 SCPs, 1 Gateway, 1 
> Battery Monitor, 1 AGS.  3000 ahr of NiFe batteries.  36 kW Kubota 
> Genset.
> 
> I tried using the Inverter SCP to program settings on the new inverters 
> and it took everything but when I checked on InsightLocal the settings 
> had not changed.  They were all still default so I had to go through it 
> again one at a time through insightlocal.  I'm guessing the SCP no 
> longer works for programming with the Gateway?  Can anyone confirm?  
> Programming used to work through the SCP with the old XW+ inverters and 
> firmware.
> 
> Tried using the Solar SCP to change settings on the charge controls but 
> had to use insight local to change each individually.  Used to be able 
> to use  the "copy from" function which was a real time saver.  
> Wondering if anyone else has run into the same problem, or if it works 
> for them, what am I missing?  Is there a cool way to change one setting 
> with insightlocal and get it to change the other 17?
> 
> Observations:
> - looking at the CC's via insightlocal,
> under configuration -> advanced ->controls - I set all chargers 
> "enabled" but the next day or so they all go to "disabled".  They all 
> still work though.  Doesn't seem to affect operations.
> 
> under configuration -> advanced ->charger settings - I have the first 
> CC set to "primary" and the rest to secondary.  No idea if that's right 
> or not.  seems to work.  Options are "stand-alone, primary, secondary 
> and echo".  I could not find definitions in the manual on them.
> 
> - looking at the XW Pros via insight local,
> under configuration -> advanced ->controls -> Backup Mode - I disabled 
> BAckup mode since I'm not backing up the grid. System shut down 
> immediately.  Backup mode must be enabled when you're off grid.
> 
> Thanks in advance : )
> 
> Greg Egan
> Remote Power Inc
> Fairbanks, AK
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try 
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20230611/bf293e79/attachment.htm>


More information about the RE-wrenches mailing list