[RE-wrenches] SolArk and Tigo compatibility
    Nick A Lucchese 
    lucchesesolar at me.com
       
    Wed Nov 16 09:38:39 PST 2022
    
    
  
All, I believe what Chris is referring to is something I was initially confused on during a Solark install I was involved with last year. Uncertain if the manual has changed but in the Solark 12k manual dated April 2, 2021 on page 23 it has a line saying-
Note: Tigo Optimizers are compatible with the Sol-Ark 12k (Do not use the built in 12v Power supply in the Sol-Ark user area to power the Tigo Optimizer TX transmitter)
I too had to confirm with Sol-Ark to clarify these details. I’ve not looked at any of their newer manuals to see if some of these notes have changed.
Enjoy your day, Nick
> On Nov 16, 2022, at 8:41 AM, Chris Sparadeo via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
> 
> Hi Chris,
> 
> I echo Ronald’s experience. I wasn’t aware of any memo from Sol Ark suggesting pins 15 and 16 should not be used for the Tigo RSS Transmitter. The 12K and 15K manuals both refrence a 12vdc RSS transmitter to achieve rapid shut down. 
> 
> Best,
> 
> Chris 
> 
> On Wed, Nov 16, 2022 at 11:21 AM Roland - RES via RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org>> wrote:
> Aloha Chris,
> 
> We have numerous Sol-Ark systems with Tigo TS4Fs where we have the transmitter wired to the 12v supply of the inverter, with no issues to date.
> 
>> Sent from a IPhone, with touch screen keys on the fly. Please excuse shortcuts and typos. 
>> 
> Roland Shackelford
> NABCEP CERTIFIED PV INSTALLER
> President 
> Renewable Energy Services (RES), Inc. 
> Mobile:  808-938-9239 <http://808-938-9239/>
> www.renewablenergy.com <http://www.renewablenergy.com/>
> 
>> On Nov 16, 2022, at 4:33 AM, Christopher Warfel via RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org>> wrote:
>> 
>> 
> 
>> Hi, We are doing our first system with these two devices. The inverter is SolArk 12P (mutimode) and the Tigo product for RS is the TS4F.  Tigo has me a little bit walking in         circles. 
>> 
>> I told them that SolArk says not to use the 12VDC RS output terminals for connecting the transmitter.  I gave them the attached drawing which they ask for, which shows the transmitter connected to a 120VAC/12VDC breaker which they supply.  They told me to wire the 120VAC source to the main service panel so the array would shut down on loss of power. I told them that is exactly NOTwhat I wanted to happen as that would stop the battery charging when there is a loss of utility power. I said I wanted the 120VAC source to be the back up loads panel. After about a week of calls and emails, I got an email back saying to use the SolArk 12VDC terminals for RS.  I just emailed them a screen shot of the SolArk manual that says not to do that.
>> 
>> At this point, I am asking anyone on the list to let me know how they wired the transmitter successfully. Thank you for any guidance, Chris Warfel
>> 
>> 
>> 
>> 
>> 
>> 
>> 
>> 
>> 
>> -- 
>>                                          Christopher Warfel
>>                      ENTECH Engineering, Inc.
>> PO Box 871, Block Island, RI 02807
>>                                                             401-466-8978
>>  <http://entech-engineering.com/>
>>  <http://entech-engineering.com/>
>> 
>> 
> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org <http://re-wrenches.org/>
>> 
>> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> There are two list archives for searching. When one doesn't work, try the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org <http://re-wrenches.org/>
> 
> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> 
> -- 
> Chris Sparadeo
> 
> 
> C_802-369-4458
> H_802-728-3059
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20221116/199c6b25/attachment.htm>
    
    
More information about the RE-wrenches
mailing list