Check for a loose neutral.

 

----------------------------------------------------------------------------

Dana Orzel                       Great Solar Works, Inc. 

208.721.7003                       dana at solarwork.com

Idaho Contractor - # 028765          Idaho PV # 028374

NABCEP # 051112-136                       www.solarwork.biz

"Responsible Technologies for Responsible People since 1988"  

P Please consider the environment before printing this email.

 

 

From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of August Goers
Sent: Monday, March 27, 2017 11:55 AM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Sunpower micros and mysterious outages

 

Strange one. I would be surprised if the PV system has anything to do with this. We’ve experienced strange electrical intermittent problems and they have almost always been related to grounding or neutral problems. I realize that two different electricians have checked out the site, but maybe they missed something like a loose neutral (check all the way back to the service point of connection). It might be worth calling the utility out as well incase their feed has problems.

 

August

Luminalt

 

From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org <mailto:re-wrenches-bounces at lists.re-wrenches.org> ] On Behalf Of Hilton Dier III
Sent: Monday, March 27, 2017 9:04 AM
To: re-wrenches at lists.re-wrenches.org
Subject: [RE-wrenches] Sunpower micros and mysterious outages

 

Friends of mine got a Sunpower system installed last year. Ever since then they have had intermittent problems with circuits in their house going dead.

The array is 14 each Sunpower SPR E20 327 C AC. The array is mounted on a corrugated steel roof on their garage, about 20 feet from the house.

What happens is that a circuit in their house will either go dead or brown out so lights barely glow. This happens to various circuits and at any time of day or night. The rest of the circuits will work fine and the event will last an hour or two. The breakers don't trip. They have had two different electricians there to check the house wiring and it's all solid.

Any ideas? Some kind of metal roof capacitance?

Many thanks,

Hilton

-- 
Hilton Dier III
Missisquoi River Hydro
Renewable Energy Design
453 East Hill Rd.
Middlesex, VT 05602
Tel: 802-223-6652