[RE-wrenches] Sunpower micros and mysterious outages
Ray
ray at solarray.com
Tue Mar 28 11:09:49 PDT 2017
An IR camera may be helpful. FIir has some really affordable models
now, I have the TG 167 which is plenty of resolution for electrical.
They can find problems in load centers really fast; we found an
overloaded neutral the other day we would not have noticed otherwise.
R. Ray Walters
Chief Technical Officer, RemoteSolar.com
BS Mech Engineering, 1988
Former NABCEP Certified, 2004-2016
Licensed Master ELectrician, Colorado
303 505-8760
On 3/27/17 5:49 PM, Dana wrote:
>
> Check for a loose neutral.
>
> ----------------------------------------------------------------------------
>
> Dana Orzel Great Solar Works, Inc.
>
> *208.721.7003 dana at solarwork.com*
>
> Idaho Contractor - # 028765 Idaho PV # 028374
>
> NABCEP # 051112-136 www.solarwork.biz
>
> _"Responsible Technologies for Responsible People since 1988" ___
>
> *P*Please consider the environment before printing this email.
>
> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org]
> *On Behalf Of *August Goers
> *Sent:* Monday, March 27, 2017 11:55 AM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Subject:* Re: [RE-wrenches] Sunpower micros and mysterious outages
>
> Strange one. I would be surprised if the PV system has anything to do
> with this. We’ve experienced strange electrical intermittent problems
> and they have almost always been related to grounding or neutral
> problems. I realize that two different electricians have checked out
> the site, but maybe they missed something like a loose neutral (check
> all the way back to the service point of connection). It might be
> worth calling the utility out as well incase their feed has problems.
>
> August
>
> Luminalt
>
> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org
> <mailto:re-wrenches-bounces at lists.re-wrenches.org>] *On Behalf Of
> *Hilton Dier III
> *Sent:* Monday, March 27, 2017 9:04 AM
> *To:* re-wrenches at lists.re-wrenches.org
> <mailto:re-wrenches at lists.re-wrenches.org>
> *Subject:* [RE-wrenches] Sunpower micros and mysterious outages
>
> Friends of mine got a Sunpower system installed last year. Ever since
> then they have had intermittent problems with circuits in their house
> going dead.
>
> The array is 14 each Sunpower SPR E20 327 C AC. The array is mounted
> on a corrugated steel roof on their garage, about 20 feet from the house.
>
> What happens is that a circuit in their house will either go dead or
> brown out so lights barely glow. This happens to various circuits and
> at any time of day or night. The rest of the circuits will work fine
> and the event will last an hour or two. The breakers don't trip. They
> have had two different electricians there to check the house wiring
> and it's all solid.
>
> Any ideas? Some kind of metal roof capacitance?
>
> Many thanks,
>
> Hilton
>
> --
> Hilton Dier III
> Missisquoi River Hydro
> Renewable Energy Design
> 453 East Hill Rd.
> Middlesex, VT 05602
> Tel: 802-223-6652
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20170328/b1be858c/attachment-0003.html>
More information about the RE-wrenches
mailing list