Thanks Dave, This is all helpful. We do90% battery systems, and I need 
to emphasize periodic maintenance. This will help. Chris


On 1/21/2017 10:52 AM, Dave Palumbo wrote:
>
> Hi Chris,
>
> I don't have any pictures myself, the Backwoods email included a photo 
> of a corroded bolt and a clean assembly which I've snipped and attached.
>
> Off the Wrenches list I have had a conversation with another wrench 
> who shared his successful methods which I will share here.
>
> << The issue I remember from before on this thread was do you put the 
> material between the lug and post or outside of it?
>
> And I’m not sure from the article if it was put on between or outside?
>
> Personally I’ve done between and  never had a problem. Yes I’ve seen 
> corrosion around the lug, but take the lug off and its clean.   
> Outside seals the corrosion in, inside prevents it from forming IMO.
>
> However, if the bolt got lose, it would generate heat, which would 
> melt out any and all material, creating oxidation, more heat and away 
> you go to failure mode.
>
> Also the photo doesn’t show split/lock washer.  I think its really 
> important as the lead does flow over time, so no matter how tight you 
> make it,  it will loosen up over time especially with higher 
> currents/heat.
>
> The lock washer will buy you some time before needing to retorque the 
> fasteners.
>
>  I’m curious about the damage mode to the inverter and all that.  I 
> don’t understand how a short on the battery would destroy all the 
> electronics?
>
> I’ve gone to a battery angle grinder with flappy wheel to prep the 
> terminal posts. - fast. >>
>
> My response to him.
>
> I wondered about the failure of those big expensive components too, 
> but I have never had a dead short for more than a split second at the 
> batteries (a few misplaced cables when working too quickly are easily 
> dealt with). I have been installing a catastrophic class T fuse 
> between the battery bank and the DC distribution center breaker also.
>
> I would always buff the cable ends with a green scrubbie and file the 
> battery terminals to remove any corrosion and then lightly coat all 
> surfaces,  including all the hardware thoroughly (incldng lock 
> washer), with petroleum jelly before assembling and tightening (very 
> tight - tight as I could without breaking the hardware, lead starts to 
> compress). I've been very happy with doing it this way for 30+ years. 
> Learned much of this from Peter Talmage and Rob Wills here back east 
> as well as from Richard Perez (RIP).
>
>  Dave
>
> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] 
> *On Behalf Of *cwarfel
> *Sent:* Saturday, January 21, 2017 9:54 AM
> *To:* re-wrenches at lists.re-wrenches.org
> *Subject:* Re: [RE-wrenches] Hidden corrosion caused catastrophic 
> battery system failure
>
> Hi David, do you have any pictures of this that could be shared?  Chris
>
> On 1/20/2017 12:52 PM, Dave Palumbo wrote:
>
>     Following is an entry from a Backwoods Solar email that I received
>     today. I would like to share this as a teachable point for RE
>     techs not familiar enough with proper battery bank care and as a
>     reminder for those of us with years of storage battery experience.
>
>     I have underlined the two issues in the Backwoods email copied
>     below my bullet points to highlight the teachable issues.
>
>     ·Checking wiring connections: Check not only for tightness but
>     also for temperature. There are two simple methods that work well:
>     #1) Use an IR Thermometer to ensure all connections are of a
>     similar moderate temperature. #2)  Use your fingers to check
>     temperatures. I'm practiced at this second method because
>     inexpensive IR thermometers were not available when I began to
>     care for storage batteries. I simply use my bare fingers (with a
>     light coating of petroleum jelly) to wiggle test each battery
>     cable at the battery terminal. Fingers are sensitive enough to
>     gauge proper temperature. I have easily found several warm or hot
>     connection points over the years caused by loose or corroded
>     hardware. Do this as preventive maintenance every time you water
>     the batteries or bi-monthly with sealed cells. Corrective measures
>     (tightening, or taking apart and cleaning, or replacing, and
>     reinstalling) are taken immediately when a warmer than usual
>     connection is identified.
>
>     ·It is not recommended by most veteran wrenches to use any
>     "anti-corrosion paste" on the terminal connections. This has been
>     discussed a few times over the years on the Wrenches list. Most of
>     us have found that a thin coating of petroleum jelly (Vaseline is
>     one brand) does the best job of protecting against corrosion while
>     still allowing some visual inspection.
>
>     from Backwoods Solar 1/20/17.  << This past summer Backwoods had a
>     visit from one of our retired co-workers, xxxxx.  While it is
>     always good to have friends visit, the circumstances for his
>     dropping by were less than ideal.
>
>     A small, catastrophic failure had led to the loss of a battery
>     bank, two inverters, and a voltage converter.  Ultimately, the
>     failure was traced back to a single nut and bolt in the battery
>     bank cable connections, that had developed hidden corrosion over
>     time.  Corrosion causes resistance to the flow of electricity,
>     which in turn generates heat.  With enough corrosion, and enough
>     current flow, the amount of heat generated can be sufficient to
>     melt battery terminal connections; which is exactly what happened
>     in xxxxx’s case.  The melted metal flowed between the negative and
>     positive terminals of his industrial battery, causing a high power
>     short that was beyond the capabilities of any of the circuit
>     protection, resulting in the damage to the equipment.
>
>     Now keep in mind, xxxxx is one of the more detail-oriented people
>     we’ve had here at Backwoods.  The discipline of a military
>     background, along with critical thinking of an engineer, were
>     still not enough to overlook one very tiny detail.  xxxxx does his
>     mechanical maintenance on a routine schedule; _checking for
>     tightness in wiring connections_, cleaning accumulated spray off
>     battery tops, cleaning out dust and spider webs, _and keeping his
>     battery terminal posts coated with anti-corrosion paste._  This is
>     not the type of person you’d expect to see such a failure.
>
>     So what happened?  It all boiled down to the battery terminal
>     connections.  What xxxxx had NOT done, was dissembled the nut and
>     bolts from the battery terminals and cables to check for internal,
>     hidden corrosion.  It had been about 6 years since he had done
>     that level of inspection.  When previously reviewed, the hardware
>     had been thoroughly inspected, cleaned, and re-assembled, and then
>     coated with _anti-corrosion paste on the exterior_.  In one of the
>     16 nut/bolt pairs, a small bit of contamination or moisture must
>     have been left trapped inside.  Over the course of the next six
>     years, the corrosion grew, contaminating the entire connection;
>     but was NOT visible externally at all! >>
>
>     Best regards,
>
>     Dave
>
>     David Palumbo
>
>     Independent Power LLC
>
>     462 Solar Way Drive
>
>     Hyde Park, VT 05655
>
>     802-371-8678 cell
>
>     802-888-4917 home
>
>
>
>
>     _______________________________________________
>
>     List sponsored by Redwood Alliance
>
>     List Address:RE-wrenches at lists.re-wrenches.org
>     <mailto:RE-wrenches at lists.re-wrenches.org>
>
>     Change listserver email address & settings:
>
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>     List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>     List rules & etiquette:
>
>     www.re-wrenches.org/etiquette.htm
>     <http://www.re-wrenches.org/etiquette.htm>
>
>     Check out or update participant bios:
>
>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
> -- 
> Christopher Warfel, PE
> Entech Engineering, Inc.
> 401-466-8978
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>

-- 
Christopher Warfel, PE
Entech Engineering, Inc.
401-466-8978

-------------- next part --------------