[RE-wrenches] 690.8
Drake
drake.chamberlin at redwoodalliance.org
Thu Nov 10 06:48:04 PST 2016
When using acronyms,please use entire phrase at
least once, such as "Permit and Resource
Management Department (PRMD)." Those of us who
don't live in Sonoma County (or even California)
might not know what it means. This one readily
showed up with an Internet search. Some of the
acronyms used on the list aren't so easy to find.
Thank you,
Drake
At 08:57 PM 11/9/2016, you wrote:
>Wrenches
>We are getting some questions from PRMD some
>questions relating to 690.8 here is what we have
>3 modules, 260 watts at 9 amps ISC each module is a single string which
>goes into a MNPV6 disco/combiner/disconnect
>combined to a 30 amp breaker, it is being
>replaced with a 40 amp per 690.8(A) 1
>leaves there and goes to a 32 amp disconnect in our device.
>here is where it gets interesting
>690.8 (A) requires the 40 amp breaker but reading down to 690.8 (B) 1 we
>need to up-size to 50 amps (no 45 amp is non available)
>We also have added the 63 amp GFI in the disco
>we have also moved up from # 10 wire to # 8 wire as a result
>All this seams over kill for three modules,
>there are 2 exceptions but PRMD do
>not feel they are relative.
>Is the Midnite solar disco considered an
>assembly with the bus bars inside if we install the breakers
>Any ideas would be helpful
>Jerry
>
>Â
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
>www.members.re-wrenches.org
---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
More information about the RE-wrenches
mailing list