[RE-wrenches] Rapid Shutdown

Ray Walters ray at solarray.com
Tue Mar 15 17:23:15 PDT 2016


Hi Brad;

I think that remotely tripping the inverter might work with Outback, but 
definitely not with Magnum. (I checked with them today) Also, if the 
battery cables are more than 5 ft long, the rapid disconnect /might/ 
have to be closer to the batteries.  (/690.12 ...shall apply only to PV 
system conductors more than 5 ft in length inside the building...)

/As for inverter and overall system reliability? I'm afraid that//is 
going 'Rapidly' down hill.// Decades//of experience says that the more 
gizmos and automatic controls you add, the more chances you have for 
something to go wrong.  The Birdhouse system defaults to/'off' /with any 
communications problems, so one CAT 5 cable has a nick in it, and the 
entire system crashes.//With all this emphasis on safety, we also need 
to be thinking about our customers living alone in cold, remote locations./
/Perhaps an emergency disconnect for the emergency disconnect?

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 3/15/2016 5:45 PM, Bradley Bassett wrote:
> I've been promoting the use of the remote on/off terminals that are 
> available in most inverters, which can be connected to the AUX in the 
> Birdhouse. For a very minimum effort and cost, the inverter AC output 
> would be shutdown when the rapid shutdown is activated.  I think using 
> the remote on/off terminals seems a lot cleaner way to do this than 
> disconnecting the battery cables. And there is the possibility that 
> disconnecting the battery from a fully loaded inverter may damage the 
> inverter, do we really want to risk that whenever we test the RSD 
> system? None of the current inverter mfg will say that this will do 
> any damage, but they don't seem very convinced to me. I remember a 
> decade ago when they did say there could be an issue. I'm not sure how 
> much different inverters are now than then.
>
> Brad
> AEE Solar
>
> On Tue, Mar 15, 2016 at 12:48 PM, Patrick Shortell 
> <pshortell6 at gmail.com <mailto:pshortell6 at gmail.com>> wrote:
>
>     Dear List,
>     Maybe it's an over simplistic opinion, but shouldnt all sources be
>     disconnected rapidly in an emergency situation.
>     We can always do better than what the code requires. I get
>     frustrated when people go to the book, (and try to hide behind the
>     text). instead of thinking through real life scenarios.
>     There are simple ways to work around these issues.
>     I find when something is questionable, Ill call the AHJ and get
>     his approval First.
>     What would I do in my own house?
>     What if someone thought all the power was off when they dragged a
>     hoseline into my basement.
>     My two cents
>     Pat
>
>     On Tue, Mar 15, 2016 at 1:10 PM, <billbrooks7 at sbcglobal.net
>     <mailto:billbrooks7 at sbcglobal.net>> wrote:
>
>         Ray,
>
>         I guess I have to step in after that acknowledgement. PV
>         system circuit is a
>         self-defined term and therefore cannot be defined unless you
>         are going to
>         develop a meaning that is different from the self-definition.
>         It means ANY
>         circuit in a PV system. This includes battery and stand-alone
>         circuits in
>         the 2014 NEC.
>
>         The language of the 2014 NEC was a compromise between the fire
>         service and
>         the PV industry.  Originally, the language required
>         essentially module-level
>         shutdown. I raised the concern with the PV industry to get
>         them involved
>         since most were not paying attention at the time. This
>         language was
>         developed and intended to cover all circuits in a PV system.
>         In the 2014
>         NEC, batteries are part of a PV system and therefore fall
>         under this
>         requirement.
>
>         In the 2017 NEC, we were very careful to carve out all
>         batteries and loads,
>         that were previously part of PV systems, and place them in
>         their own
>         articles. Don't shoot the messenger on this one and don't
>         think for a minute
>         that I alone made this requirement or am alone in interpreting
>         it in this
>         way. I did author this compromise with other representatives
>         of the PV
>         industry so I think I know what the intent was.
>
>         It is understandably difficult for battery systems and I would
>         try to keep
>         battery circuits as short as possible. The 5-feet was intended
>         to match the
>         requirement of 690.71(H)--which is further evidence of the
>         intent of the
>         2014 NEC.
>
>         The 2017 NEC removes batteries from the requirement, but they
>         still cannot
>         backfeed the PV array. Energy storage systems (Article 706)
>         will have their
>         own requirements in time--that is guaranteed.
>
>         Bill.
>
>
>         -----Original Message-----
>         From: RE-wrenches
>         [mailto:re-wrenches-bounces at lists.re-wrenches.org
>         <mailto:re-wrenches-bounces at lists.re-wrenches.org>] On
>         Behalf Of Ray Walters
>         Sent: Tuesday, March 15, 2016 9:02 AM
>         To: RE-wrenches <re-wrenches at lists.re-wrenches.org
>         <mailto:re-wrenches at lists.re-wrenches.org>>
>         Subject: [RE-wrenches] Rapid Shutdown
>
>         Greetings Esteemed Wrenches:
>
>         I've just heard back from our inspector here in Colorado, and
>         we are still
>         being required to disconnect the batteries under 690.12.  No
>         where in 690.12
>         are batteries mentioned, nor in the appropriate 690.71 section
>         that deals
>         with batteries.  The entire reasoning behind this is based on
>         a single
>         article written by a single person: Bill Brooks.  I have
>         contacted both
>         Outback and Magnum on this issue, and their engineers are
>         unaware that rapid
>         shutdown applies.
>         My interpretation is that I could install an inverter and
>         battery system
>         that was charged from a generator, and we would not need any
>         rapid shutdown
>         at all.  But according to Bill, as soon as I put a single
>         solar module into
>         the system, suddenly the entire system becomes PV? The problem
>         lies with the
>         term 'PV System circuit'  used in 690.12. 690.2 Defines 'PV Output
>         circuit', and 'PV source circuit', but there is no 'PV system
>         circuit'
>         defined.  690.12 therefore uses an undefined term.
>         Our design uses 2 inverters, so if we used Midnite's E panel
>         with their
>         remote trip breakers, the 2nd inverter would be more than 5 ft
>         from the
>         batteries.  If we used Magnum or Outback DC disconnects (that
>         would comply
>         with the 5 ft rule specified in 690.71) they don't offer
>         remote trip.
>         We have a Midnite Rapid disconnect Combiner on the roof with
>         the Birdhouse,
>         so we are complying with 690.12, it should not be applied to
>         batteries
>         though.
>
>         Thanks,
>
>         --
>         R.Ray Walters
>         CTO, Solarray, Inc
>         Nabcep Certified PV Installer,
>         Licensed Master Electrician
>         Solar Design Engineer
>         303 505-8760 <tel:303%20505-8760>
>
>         _______________________________________________
>         List sponsored by Redwood Alliance
>
>         List Address: RE-wrenches at lists.re-wrenches.org
>         <mailto:RE-wrenches at lists.re-wrenches.org>
>
>         Change listserver email address & settings:
>         http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>         List-Archive:
>         http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>         List rules & etiquette:
>         www.re-wrenches.org/etiquette.htm
>         <http://www.re-wrenches.org/etiquette.htm>
>
>         Check out or update participant bios:
>         www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>         _______________________________________________
>         List sponsored by Redwood Alliance
>
>         List Address: RE-wrenches at lists.re-wrenches.org
>         <mailto:RE-wrenches at lists.re-wrenches.org>
>
>         Change listserver email address & settings:
>         http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>         List-Archive:
>         http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>         List rules & etiquette:
>         www.re-wrenches.org/etiquette.htm
>         <http://www.re-wrenches.org/etiquette.htm>
>
>         Check out or update participant bios:
>         www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
>
>     -- 
>     Patrick A. Shortell
>     /Licensed Master Electrician/
>     /Certified Solar Installer/
>     71 Oregon Street
>     Long Beach N.Y. 11561
>     cell: 516-477-0221 <tel:516-477-0221>
>
>
>
>
>
>     _______________________________________________
>     List sponsored by Redwood Alliance
>
>     List Address: RE-wrenches at lists.re-wrenches.org
>     <mailto:RE-wrenches at lists.re-wrenches.org>
>
>     Change listserver email address & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>     List-Archive:
>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>     List rules & etiquette:
>     www.re-wrenches.org/etiquette.htm
>     <http://www.re-wrenches.org/etiquette.htm>
>
>     Check out or update participant bios:
>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160315/5b245b50/attachment-0002.html>


More information about the RE-wrenches mailing list