    Hi Brad;<br>
    <br>
    I think that remotely tripping the inverter might work with Outback,
    but definitely not with Magnum. (I checked with them today) Also, if
    the battery cables are more than 5 ft long, the rapid disconnect <i>might</i>
    have to be closer to the batteries.  (<i>690.12 ...shall apply only
      to PV system conductors more than 5 ft in length inside the
      building...)<br>
      <br>
    </i>As for inverter and overall system reliability? I'm afraid that<i>
    </i>is going 'Rapidly' down hill.<i> </i> Decades<i> </i>of
    experience says that the more gizmos and automatic controls you add,
    the more chances you have for something to go wrong.  The Birdhouse
    system defaults to<i> 'off' </i>with any communications problems,
    so one CAT 5 cable has a nick in it, and the entire system crashes.<i>
    </i>With all this emphasis on safety, we also need to be thinking
    about our customers living alone in cold, remote locations.<i><br>
    </i>Perhaps an emergency disconnect for the emergency disconnect?<br>
    <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
    <div class="moz-cite-prefix">On 3/15/2016 5:45 PM, Bradley Bassett
      wrote:<br>
    </div>
    <blockquote
cite="mid:CAEpjgH1LgYdamzY4oWeqSsuc7Q1sddF035nD_60O1=G4sFs4Og@mail.gmail.com"
      type="cite">
      <div dir="ltr">
        <div>
          <div>I've been promoting the use of the remote on/off
            terminals that are available in most inverters, which can be
            connected to the AUX in the Birdhouse. For a very minimum
            effort and cost, the inverter AC output would be shutdown
            when the rapid shutdown is activated.  I think using the
            remote on/off terminals seems a lot cleaner way to do this
            than disconnecting the battery cables. And there is the
            possibility that disconnecting the battery from a fully
            loaded inverter may damage the inverter, do we really want
            to risk that whenever we test the RSD system? None of the
            current inverter mfg will say that this will do any damage,
            but they don't seem very convinced to me. I remember a
            decade ago when they did say there could be an issue. I'm
            not sure how much different inverters are now than then.<br>
            <br>
          </div>
          Brad<br>
        </div>
        AEE Solar<br>
      </div>
      <div class="gmail_extra"><br>
        <div class="gmail_quote">On Tue, Mar 15, 2016 at 12:48 PM,
          Patrick Shortell <span dir="ltr"><<a
              moz-do-not-send="true" href="mailto:pshortell6@gmail.com"
              target="_blank"><a class="moz-txt-link-abbreviated" href="mailto:pshortell6@gmail.com">pshortell6@gmail.com</a></a>></span> wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex">
            <div dir="ltr">
              <div>
                <div>
                  <div>
                    <div>
                      <div>
                        <div>
                          <div>
                            <div>Dear List,<br>
                            </div>
                            Maybe it's an over simplistic opinion, but
                            shouldnt all sources be disconnected rapidly
                            in an emergency situation.<br>
                          </div>
                          We can always do better than what the code
                          requires. I get frustrated when people go to
                          the book, (and try to hide behind the text). 
                          instead of thinking through real life
                          scenarios.<br>
                        </div>
                        There are simple ways to work around these
                        issues.<br>
                      </div>
                      I find when something is questionable, Ill call
                      the AHJ and get his approval First.<br>
                    </div>
                    What would I do in my own house?<br>
                  </div>
                  What if someone thought all the power was off when
                  they dragged a hoseline into my basement.<br>
                </div>
                My two cents<br>
              </div>
              Pat<br>
            </div>
            <div class="gmail_extra">
              <div>
                <div class="h5"><br>
                  <div class="gmail_quote">On Tue, Mar 15, 2016 at 1:10
                    PM, <span dir="ltr"><<a moz-do-not-send="true"
                        href="mailto:billbrooks7@sbcglobal.net"
                        target="_blank">billbrooks7@sbcglobal.net</a>></span>
                    wrote:<br>
                    <blockquote class="gmail_quote" style="margin:0 0 0
                      .8ex;border-left:1px #ccc solid;padding-left:1ex">Ray,<br>
                      <br>
                      I guess I have to step in after that
                      acknowledgement. PV system circuit is a<br>
                      self-defined term and therefore cannot be defined
                      unless you are going to<br>
                      develop a meaning that is different from the
                      self-definition. It means ANY<br>
                      circuit in a PV system. This includes battery and
                      stand-alone circuits in<br>
                      the 2014 NEC.<br>
                      <br>
                      The language of the 2014 NEC was a compromise
                      between the fire service and<br>
                      the PV industry.  Originally, the language
                      required essentially module-level<br>
                      shutdown. I raised the concern with the PV
                      industry to get them involved<br>
                      since most were not paying attention at the time.
                      This language was<br>
                      developed and intended to cover all circuits in a
                      PV system. In the 2014<br>
                      NEC, batteries are part of a PV system and
                      therefore fall under this<br>
                      requirement.<br>
                      <br>
                      In the 2017 NEC, we were very careful to carve out
                      all batteries and loads,<br>
                      that were previously part of PV systems, and place
                      them in their own<br>
                      articles. Don't shoot the messenger on this one
                      and don't think for a minute<br>
                      that I alone made this requirement or am alone in
                      interpreting it in this<br>
                      way. I did author this compromise with other
                      representatives of the PV<br>
                      industry so I think I know what the intent was.<br>
                      <br>
                      It is understandably difficult for battery systems
                      and I would try to keep<br>
                      battery circuits as short as possible. The 5-feet
                      was intended to match the<br>
                      requirement of 690.71(H)--which is further
                      evidence of the intent of the<br>
                      2014 NEC.<br>
                      <br>
                      The 2017 NEC removes batteries from the
                      requirement, but they still cannot<br>
                      backfeed the PV array. Energy storage systems
                      (Article 706) will have their<br>
                      own requirements in time--that is guaranteed.<br>
                      <br>
                      Bill.<br>
                      <div>
                        <div><br>
                          <br>
                          -----Original Message-----<br>
                          From: RE-wrenches [mailto:<a
                            moz-do-not-send="true"
                            href="mailto:re-wrenches-bounces@lists.re-wrenches.org"
                            target="_blank"><a class="moz-txt-link-abbreviated" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a></a>]
                          On<br>
                          Behalf Of Ray Walters<br>
                          Sent: Tuesday, March 15, 2016 9:02 AM<br>
                          To: RE-wrenches <<a moz-do-not-send="true"
href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>><br>
                          Subject: [RE-wrenches] Rapid Shutdown<br>
                          <br>
                          Greetings Esteemed Wrenches:<br>
                          <br>
                          I've just heard back from our inspector here
                          in Colorado, and we are still<br>
                          being required to disconnect the batteries
                          under 690.12.  No where in 690.12<br>
                          are batteries mentioned, nor in the
                          appropriate 690.71 section that deals<br>
                          with batteries.  The entire reasoning behind
                          this is based on a single<br>
                          article written by a single person: Bill
                          Brooks.  I have contacted both<br>
                          Outback and Magnum on this issue, and their
                          engineers are unaware that rapid<br>
                          shutdown applies.<br>
                          My interpretation is that I could install an
                          inverter and battery system<br>
                          that was charged from a generator, and we
                          would not need any rapid shutdown<br>
                          at all.  But according to Bill, as soon as I
                          put a single solar module into<br>
                          the system, suddenly the entire system becomes
                          PV? The problem lies with the<br>
                          term 'PV System circuit'  used in 690.12. 
                          690.2 Defines 'PV Output<br>
                          circuit', and 'PV source circuit', but there
                          is no 'PV system circuit'<br>
                          defined.  690.12 therefore uses an undefined
                          term.<br>
                          Our design uses 2 inverters, so if we used
                          Midnite's E panel with their<br>
                          remote trip breakers, the 2nd inverter would
                          be more than 5 ft from the<br>
                          batteries.  If we used Magnum or Outback DC
                          disconnects (that would comply<br>
                          with the 5 ft rule specified in 690.71) they
                          don't offer remote trip.<br>
                          We have a Midnite Rapid disconnect Combiner on
                          the roof with the Birdhouse,<br>
                          so we are complying with 690.12, it should not
                          be applied to batteries<br>
                          though.<br>
                          <br>
                          Thanks,<br>
                          <br>
                          --<br>
                          R.Ray Walters<br>
                          CTO, Solarray, Inc<br>
                          Nabcep Certified PV Installer,<br>
                          Licensed Master Electrician<br>
                          Solar Design Engineer<br>
                          <a moz-do-not-send="true"
                            href="tel:303%20505-8760"
                            value="+13035058760" target="_blank">303
                            505-8760</a><br>
                          <br>
_______________________________________________<br>
                          List sponsored by Redwood Alliance<br>
                          <br>
                          List Address: <a moz-do-not-send="true"
                            href="mailto:RE-wrenches@lists.re-wrenches.org"
                            target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
                          <br>
                          Change listserver email address &
                          settings:<br>
                          <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                            rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                          <br>
                          List-Archive:<br>
                          <a moz-do-not-send="true"
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
                            rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
                          <br>
                          List rules & etiquette:<br>
                          <a moz-do-not-send="true"
                            href="http://www.re-wrenches.org/etiquette.htm"
                            rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
                          <br>
                          Check out or update participant bios:<br>
                          <a moz-do-not-send="true"
                            href="http://www.members.re-wrenches.org"
                            rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
                          <br>
_______________________________________________<br>
                          List sponsored by Redwood Alliance<br>
                          <br>
                          List Address: <a moz-do-not-send="true"
                            href="mailto:RE-wrenches@lists.re-wrenches.org"
                            target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
                          <br>
                          Change listserver email address &
                          settings:<br>
                          <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                            rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                          <br>
                          List-Archive: <a moz-do-not-send="true"
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
                            rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
                          <br>
                          List rules & etiquette:<br>
                          <a moz-do-not-send="true"
                            href="http://www.re-wrenches.org/etiquette.htm"
                            rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
                          <br>
                          Check out or update participant bios:<br>
                          <a moz-do-not-send="true"
                            href="http://www.members.re-wrenches.org"
                            rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
                          <br>
                        </div>
                      </div>
                    </blockquote>
                  </div>
                  <br>
                  <br clear="all">
                  <br>
                </div>
              </div>
              <span class="HOEnZb"><font color="#888888">-- <br>
                  <div>
                    <div dir="ltr">
                      <div>
                        <div dir="ltr">
                          <div dir="ltr">Patrick A. Shortell
                            <div><i>Licensed Master Electrician</i></div>
                            <div><i>Certified Solar Installer</i></div>
                            <div>71 Oregon Street</div>
                            <div>Long Beach N.Y. 11561</div>
                            <div>cell: <a moz-do-not-send="true"
                                href="tel:516-477-0221"
                                value="+15164770221" target="_blank">516-477-0221</a></div>
                            <div><br>
                            </div>
                            <div><br>
                            </div>
                            <div><br>
                            </div>
                            <div><br>
                            </div>
                          </div>
                        </div>
                      </div>
                    </div>
                  </div>
                </font></span></div>
            <br>
            _______________________________________________<br>
            List sponsored by Redwood Alliance<br>
            <br>
            List Address: <a moz-do-not-send="true"
              href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
            <br>
            Change listserver email address & settings:<br>
            <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
              rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
            <br>
            List-Archive: <a moz-do-not-send="true"
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
              rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
            <br>
            List rules & etiquette:<br>
            <a moz-do-not-send="true"
              href="http://www.re-wrenches.org/etiquette.htm"
              rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
            <br>
            Check out or update participant bios:<br>
            <a moz-do-not-send="true"
              href="http://www.members.re-wrenches.org" rel="noreferrer"
              target="_blank">www.members.re-wrenches.org</a><br>
            <br>
            <br>
          </blockquote>
        </div>
        <br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>