[RE-wrenches] Rapid Shutdown

Starlight Solar Power Systems larry at starlightsolar.com
Tue Mar 15 15:19:08 PDT 2016


This is from the spec sheet:

"Hermetically sealed – UL listed: UL1604 for Class I & II, Div 2 and Class III for use in hazardous
locations, IP67 for temporary water immersion for 30 min, IP69K for perssure washing, SAE J1171 - external ignition protection, and ISO8846 for protection against ignition around flammable gasses."

No enclosure, just the solenoid as shown:


On Mar 15, 2016, at 2:47 PM, Ray Walters <ray at solarray.com> wrote:

All right Larry, that's an actual start to a solution.  My comments:
1)  We already have had a solution for the array side using a Midnite Birdhouse and Midnite rapid disconnecting combiner box.  (The PV Circuit of the "PV system circuit" so I wasn't questioning that)
2) Who is the supplier of the 400 amp solenoid, 
3) is it UL listed for Rapid disconnect, 
4) does it have an approved enclosure? (ie. does the solenoid comes mounted in a UL listed assembly)

Thanks,
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 3/15/2016 2:57 PM, Starlight Solar Power Systems wrote:
> I thought this idea (attached) was a simple solution for array and battery rapid shutdown using a Classic controller and solenoids. The PV solenoids are 350 amp continuous @ 700 Vdc, and 400A @ 48 volts for the battery. Cost is about $120 each. 
> 
> Midnite told me than plan to implement the arc fault relay control. A simple SPST switch in series with the 12 volt Aux output will allow shutdown. Add a fire alarm output relay for auto-shutdown in case of fire. Seems like a simple, cost effective way to me.
> 
> Any comments Ray, Pete, Bill?
> 
> 
> 
> <Mail Attachment.png>
> 
> Larry Crutcher
> Starlight Solar Power Systems
> 
> 
> 
> 
> On Mar 15, 2016, at 12:48 PM, Patrick Shortell <pshortell6 at gmail.com> wrote:
> 
> Dear List,
> Maybe it's an over simplistic opinion, but shouldnt all sources be disconnected rapidly in an emergency situation.
> We can always do better than what the code requires. I get frustrated when people go to the book, (and try to hide behind the text).  instead of thinking through real life scenarios.
> There are simple ways to work around these issues.
> I find when something is questionable, Ill call the AHJ and get his approval First.
> What would I do in my own house?
> What if someone thought all the power was off when they dragged a hoseline into my basement.
> My two cents
> Pat
> 
> On Tue, Mar 15, 2016 at 1:10 PM, <billbrooks7 at sbcglobal.net> wrote:
> Ray,
> 
> I guess I have to step in after that acknowledgement. PV system circuit is a
> self-defined term and therefore cannot be defined unless you are going to
> develop a meaning that is different from the self-definition. It means ANY
> circuit in a PV system. This includes battery and stand-alone circuits in
> the 2014 NEC.
> 
> The language of the 2014 NEC was a compromise between the fire service and
> the PV industry.  Originally, the language required essentially module-level
> shutdown. I raised the concern with the PV industry to get them involved
> since most were not paying attention at the time. This language was
> developed and intended to cover all circuits in a PV system. In the 2014
> NEC, batteries are part of a PV system and therefore fall under this
> requirement.
> 
> In the 2017 NEC, we were very careful to carve out all batteries and loads,
> that were previously part of PV systems, and place them in their own
> articles. Don't shoot the messenger on this one and don't think for a minute
> that I alone made this requirement or am alone in interpreting it in this
> way. I did author this compromise with other representatives of the PV
> industry so I think I know what the intent was.
> 
> It is understandably difficult for battery systems and I would try to keep
> battery circuits as short as possible. The 5-feet was intended to match the
> requirement of 690.71(H)--which is further evidence of the intent of the
> 2014 NEC.
> 
> The 2017 NEC removes batteries from the requirement, but they still cannot
> backfeed the PV array. Energy storage systems (Article 706) will have their
> own requirements in time--that is guaranteed.
> 
> Bill.
> 
> 
> -----Original Message-----
> From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
> Behalf Of Ray Walters
> Sent: Tuesday, March 15, 2016 9:02 AM
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Subject: [RE-wrenches] Rapid Shutdown
> 
> Greetings Esteemed Wrenches:
> 
> I've just heard back from our inspector here in Colorado, and we are still
> being required to disconnect the batteries under 690.12.  No where in 690.12
> are batteries mentioned, nor in the appropriate 690.71 section that deals
> with batteries.  The entire reasoning behind this is based on a single
> article written by a single person: Bill Brooks.  I have contacted both
> Outback and Magnum on this issue, and their engineers are unaware that rapid
> shutdown applies.
> My interpretation is that I could install an inverter and battery system
> that was charged from a generator, and we would not need any rapid shutdown
> at all.  But according to Bill, as soon as I put a single solar module into
> the system, suddenly the entire system becomes PV? The problem lies with the
> term 'PV System circuit'  used in 690.12.  690.2 Defines 'PV Output
> circuit', and 'PV source circuit', but there is no 'PV system circuit'
> defined.  690.12 therefore uses an undefined term.
> Our design uses 2 inverters, so if we used Midnite's E panel with their
> remote trip breakers, the 2nd inverter would be more than 5 ft from the
> batteries.  If we used Magnum or Outback DC disconnects (that would comply
> with the 5 ft rule specified in 690.71) they don't offer remote trip.
> We have a Midnite Rapid disconnect Combiner on the roof with the Birdhouse,
> so we are complying with 690.12, it should not be applied to batteries
> though.
> 
> Thanks,
> 
> --
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer,
> Licensed Master Electrician
> Solar Design Engineer
> 303 505-8760
> 
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: 
> RE-wrenches at lists.re-wrenches.org
> 
> 
> Change listserver email address & settings:
> 
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> 
> List rules & etiquette:
> 
> www.re-wrenches.org/etiquette.htm
> 
> 
> Check out or update participant bios:
> 
> www.members.re-wrenches.org
> 
> 
> 

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160315/79445e9a/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Screen Shot 2016-03-15 at 3.18.38 PM.png
Type: image/png
Size: 69963 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160315/79445e9a/attachment-0004.png>


More information about the RE-wrenches mailing list