Your assumption is the rule here. Metal inside a building envelope and it cannot transition at the penetration it must be metal before entry.
----------------------------------------------------------------------------
Dana Orzel
Great Solar Works, Inc - NABCEP # 051112-136
E - dana at solarwork.com - Web - solarwork.com
O - 970.626.5253 C - 208.721.7003
"Responsible Technologies for Responsible People since 1988"
Please consider the environment before printing this email.
-----Original Message-----
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Christopher Warfel
Sent: Monday, July 13, 2015 10:59 AM
To: re-wrenches at lists.re-wrenches.org
Subject: [RE-wrenches] DC conductors in metallic raceway/conduit
I was under the assumption that dc conductors could only be run inside a building when in metallic raceway/conduit (up to a readily accessible
disconnect switch) . The building being occupied/residence. A
contractor ran 5 feet of pvc from the wall penetration to the charge controller in a concrete block garage. I don't see anything that allows this by what I find in the NEC. Has anyone have a reference that permits this? Thank you for any assistance.
--