Your assumption is the rule here. Metal inside a building envelope and it cannot transition at the penetration it must be metal before entry.

----------------------------------------------------------------------------
Dana Orzel 
Great Solar Works, Inc -  NABCEP # 051112-136
E - dana at solarwork.com  - Web - solarwork.com 
O - 970.626.5253  C - 208.721.7003
"Responsible Technologies for Responsible People since 1988"  
 Please consider the environment before printing this email.



-----Original Message-----
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Christopher Warfel
Sent: Monday, July 13, 2015 10:59 AM
To: re-wrenches at lists.re-wrenches.org
Subject: [RE-wrenches] DC conductors in metallic raceway/conduit

I was under the assumption that dc conductors could only be run inside a building when in metallic raceway/conduit (up to a readily accessible 
disconnect switch) .  The building being occupied/residence.    A 
contractor ran 5 feet of pvc from the wall penetration to the charge controller in a concrete block garage.  I don't see anything that allows this by what I find in the NEC. Has anyone have a reference that permits this?  Thank you for any assistance.



--