[RE-wrenches] DC conductors in metallic raceway/conduit
Christopher Warfel
cwarfel at entech-engineering.com
Mon Jul 13 09:58:40 PDT 2015
I was under the assumption that dc conductors could only be run inside a
building when in metallic raceway/conduit (up to a readily accessible
disconnect switch) . The building being occupied/residence. A
contractor ran 5 feet of pvc from the wall penetration to the charge
controller in a concrete block garage. I don't see anything that allows
this by what I find in the NEC. Has anyone have a reference that permits
this? Thank you for any assistance.
--