Having the LVD be temperature compensated so that the load is always 
disconnected above the freeze point of the battery would be a Huge 
Improvement on the whole concept of LVD.  In combination with State of 
Charge monitoring, like the Whiz bang Jr, would be the most effective, 
and just program the disconnect to stay above freezing for a typical 
lead acid battery.  I got this from a Trojan White Paper:

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760


>
> FLA batteries will freeze easier if they are discharged.  I suppose 
> that you could
> use the battery temp sensor to make sure you charge them up good when
> the temp gets cold enough.
>
> boB