[RE-wrenches] Outback AGS & eq
Matt James
mjames at outbackpower.com
Fri Feb 13 09:17:49 PST 2015
Hi All,
I confirmed that a Mate3 with 002.017.000 firmware or later will stop after an EQ cycle if the AGS gen control function is changed from Manual to Auto after the genny is started.
It may also work with earlier firmware revs, but I only had a 2.17 rev close by for testing.
Matt James
Applications Engineering Manager
OutBack Power Technologies Inc.
Direct: (360) 618-4364
Cell: (360) 618-2869
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Steve Higgins
Sent: Thursday, February 12, 2015 8:28 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Outback AGS & eq
Hey guys,
For me this was a long, long time ago….But I figured that I’d chime in on the subject.
Yes Technically if you do as Jay says it’ll work… There was one firmware version of the mate that this was changed (One of the early 4.?? versions) or fixed, then it was “re-fixed” shortly thereafter, as it was a feature that was unintended.
If you have the most recent Mate firmware revision (Mate2, Mate) it’ll work this way. I do not know about the Mate3 as I left Outback shortly after the Mate 3 was released.
Steve Higgins
Technical Services Manager
P: +1.902.597.4020
M: +1.206.790.5840
F: +1.902.597.8447
Surrette Battery Company
Exclusive manufacturer of
[cid:image002.jpg at 01D0476D.2B76AEB0]<http://www.rollsbattery.com>
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of dan at foxfire-energy.com<mailto:dan at foxfire-energy.com>
Sent: Thursday, February 12, 2015 4:07 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Outback AGS & eq
Seems I was once told that (Depending on software revision), successful Switching from Manual to Auto depended on whether or not the system itself called for a start to begin with i.e. whether the start criteria was met in either AGS or a charge mode when the genny was started in manual. My problem was the customer just wanted to run the genset periodically to top off the batteries.. He would start the genny in manual (from the mate 2), and as soon as he kicked it into auto, the genny would shut down. As i recall, we found the smoking gun under timers.. If a clock was still running (Or stopped short) you could switch to auto and it would run out the clock. But if the timers were satisfied, AGS would shut down the genny.
Good Luck
db
Dan Brown
Foxfire Energy Corp.
Renewable Energy Systems
(802)-483-2564
www.Foxfire-Energy.com<http://www.Foxfire-Energy.com>
NABCEP #092907-44
[cid:image003.png at 01D0476D.2B76AEB0]
-------- Original Message --------
Subject: Re: [RE-wrenches] Outback AGS & eq
From: William Miller <william at millersolar.com<mailto:william at millersolar.com>>
Date: Thu, February 12, 2015 6:27 pm
To: RE-wrenches <re-wrenches at lists.re-wrenches.org<mailto:re-wrenches at lists.re-wrenches.org>>
Mac:
Apparently so, but this operation is not supported. It supposedly works.
William
On Feb 12, 2015, at 3:18 PM, Mac Lewis <maclewis1 at gmail.com<mailto:maclewis1 at gmail.com>> wrote:
Hi Jay & William,
Just so I understand, you can put the mate into auto right after the eq is enabled (not after eq has finished), and it will manage the generator? Is that right?
Thanks
On Thu, Feb 12, 2015 at 10:45 AM, jay peltz <jay at asis.com<mailto:jay at asis.com>> wrote:
I"ve had clients do it for years with no problems that I know of.
jay
peltz power
On Feb 12, 2015, at 9:47 AM, <william at millersolar.com<mailto:william at millersolar.com>> wrote:
Friends:
I understood the generator had to be started and stopped manually. I have a client who was using the sequence below to stop the generator automatically. To have the generator stop automatically has a convenience factor, but I do like my clients to verify the cycle has accomplished the prescribed regimen, and walking away from the process does not accomplish that.
I spoke with Outback regarding the procedure of engaging the auto mode prior to completion of the EQ and the reply was that the system had not been engineered to operate this way so the results could not be guaranteed.
William
From: RE-wrenches [mailto:re-<mailto:re->wrenches-bounces at lists.re-wrenches.org<mailto:wrenches-bounces at lists.re-wrenches.org>] On Behalf Of jay peltz
Sent: Thursday, February 12, 2015 8:54 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Outback AGS & eq
Hi Mac
I don't think there is a global eq function.
Eq continues to be manual on inverters.
Gen to manual on
Initiate EQ
Gen to auto
Done
Jay
Peltz power.
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
--
Mac Lewis
"Yo solo sé que no sé nada." -Sócrates
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
________________________________
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
This email and its attachments have been scanned by mailWatch E-Mail Firewall for viruses, spam, and malicious content. The information transmitted in this email is intended only for the entity or person to which it is addressed and may contain confidential/privileged material. If you received this in error, please contact the sender and delete the material from any computer. Any review, retransmission, dissemination, or other use of this information by persons or entities other than the intended recipient is strictly prohibited
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150213/e3f30806/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 11941 bytes
Desc: image002.jpg
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150213/e3f30806/attachment-0005.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 25138 bytes
Desc: image003.png
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150213/e3f30806/attachment-0005.png>
More information about the RE-wrenches
mailing list