4/0 copper is good for a 24V, 4000 W inverter. What is being used for
multiple inverters?

I've paralleled 4/0 into outback boxes using 2, 2" PVC conduits. It gets
pretty messy trying to put 4 sets of 4/0s into enclosures and battery
boxes (although I have worked on such systems). Does anyone have clean
solutions for these systems?

Thanks,

Drake





> Some other things:  If you keep the conduit less than 24" long, which is
> recommended anyway for main battery connections, the conduit fill
> requirements don't apply. (see exception: 310.15(B)3a2)
> Using table 310.15(B)16 yeilds 230 amps for 4/0 at 75 C.  Then 240.6
> lists 250 amp as the next standard size of OCPD which is allowed to be
> used by 240.4(B)  So you can just justify 4/0.
> Further, many manufacturers (like Midnite) use the open air ampacity
> table: 310.15(B)17, since the cable is not "in conduit" and 4/0 cable at
> 75 C is rated to 360 amps.
> The Free Air interpretation is not completely substantiated in the code
> from my read of it though.  Maybe someone more knowledgable could cite
> the chapter and verse that defines when the free air rating can and
> cannot be used.
> Also remember those breakers are 100% duty cycle rated, and that the
> inverter usually can't run any where close to 250 amps continuously.
> Bottomline is we've been using 4/0 with 250 amp breakers for almost 20
> years, and I've never seen or heard of a problem.
>
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer,
> Licensed Master Electrician
> Solar Design Engineer
> 303 505-8760
>
> On 1/1/2015 7:23 PM, jay peltz wrote:
>> Happy new year all.
>>
>> I have a question on wire sizing for the following.
>>
>> 250 amp breaker, in a UL enclosure ( say midnite or outback etc)
>> conduit from battery box to enclosure
>>
>> I'm wondering how folks size this for ampacity not voltage drop.
>>
>> thanks
>>
>> jay
>>
>> peltz power
>>
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>





More information about the RE-wrenches mailing list