The method by which inverters are able to control AC coupled power flow is
the same as used throughout the grid. The essence of it is based on a
characteristic of rotating generating machines, (generators whether motor
driven, hydro driven or other). This characteristic is that generators
slow down when they are overloaded and speed up when they are under
loaded.
Here's a link to an interesting BBC video about grid management which
shows this frequency effect on a GW grid scale.
http://www.bbc.co.uk/britainfromabove/stories/people/teatimebritain.shtml
This happens at small scale too and an inverter can be made to
automatically lower its output power when the AC frequency increases.
Victron and SMA were the first to use this to achieve AC controlled AC
coupled charging and it will also work with generators, although due to
the widely varying power/frequency characteristics of generators setting
it up can be very challenging.
I was not aware that there were older SI's which allowed a generator
connect function, as although possible if things are set up appropriately,
it will not work with every type of generator. Perhaps they stopped
allowing it due to setup frustrations.
Here's a very good paper from Victron Energy about the interaction of
generators and inverters. It has test results on efficiency, fuel
consumption, output distortion, power/frequency characteristics, AC
coupling, etc.
On our part at Schneider, the XW does not have this frequency controlled
AC coupled function but the new XW+ does have it, although we will not
support it for use with generators due to the wide variations in generator
frequency/power behavior. In the future things may change.
JARMO
_____________________________________________________________________________________
Jarmo Venalainen | Schneider Electric | Solar Business | CANADA |
Training & Development Specialist - Senior
Phone: +604-422-2528 | Fax: +604-420-1591 | Mobile: +604-505-0291
Email: jarmo.venalainen at schneider-electric.com | Site: www.SEsolar.com
| Address: 3700 Gilmore Way, Burnaby, BC V5G4M1
*** Please consider the environment before printing this e-mail
From:
Jay Peltz <jay at asis.com>
To:
RE-wrenches <re-wrenches at lists.re-wrenches.org>,
Date:
09/19/2014 06:35 AM
Subject:
Re: [RE-wrenches] Sunny Island sending power to the generator??
Sent by:
"RE-wrenches" <re-wrenches-bounces at lists.re-wrenches.org>
There is a setting in some older SI that allows for generator back feed,
no idea why. It's not in the newest version that I can find (euro).
I had to fix a system ( not mine) and once that setting was fixed no more
genny issues.
But overall I believe this inverter has a totally different way it handles
the generator vs other inverters, ( it has to) so
I'm not sure I agree with the email from Schneider.
Jay
Peltz power
Sent from my iPhone
On Sep 19, 2014, at 6:11 AM, Tump <tump at swnl.net> wrote:
I too must agree with Kevin, SMA & SI is the kind! (although I have had a
few fail) SMA IS the ONLY company that will expedite new inverter AND
compensate monetarily, not just talk but they DO. Yeah its a bit&H when
the installs are on islands cause their heavy but quality IS there,
support IS there and their Tech support does acknowledge that the manual
is complicated and there are places that exist in the manual that don't
exist in the inverter but they are very patient, (uncomplaining, tolerant,
resigned, stoical;calm, composed, even-tempered, imperturbable,
unexcitable, accommodating,understanding, indulgent; informal unflappable,
cool.)and the product is well worth the additional up front costs! ......
No I don't work for SMA!
On Sep 18, 2014, at 7:45 PM, Kevin Pegg wrote:
Our firm has installed many Sunny Island hybrid gen cycle charge systems.
In my experience they are hands down the most reliable inverter system out
there for this application. Many sites that have been working perfectly
with 100% uptime over several years. Most sites we visit once a year to
check and there are no issues at all.
There are many small tricks on the install side to get to reliability like
that. While the menus with the 8 characters and all manner of acronyms can
be daunting, once it's configured there's generally no changes needed.
Tying in the webbox option makes it a lot friendlier to program and
monitor.
My direct experience does not match with the last paragraph comments. The
only problematic installs we have worked on were installed by others and
not installed well.
Kevin Pegg
EA Energy Alternatives Ltd.
37471 Hwy 16 E
Telkwa, BC V0J 2X2
250-846-9888
Http://www.EnergyAlternatives.ca
-----Original Message-----
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org]On
Behalf Of William Miller
Sent: September 17, 2014 10:23 PM
To: RE-wrenches
Subject: [RE-wrenches] Sunny Island sending power to the generator??
Colleagues:
I was invited to troubleshoot a Sunny Island system. What I found is a
Sunny Island mini-grid system behaving oddly. The generator, when started
with the SI, would run for a few minutes and then shut down. Further
investigation revealed that the SIs were indicating that the inverters
were sending lots of power back to the generator, even with the Sunny Boy
turned off.
I don’t know if this was actually the case, nor can I grasp how this could
happen. The system was programmed as a PV/Gen only system. Fortunately I
reached an off-grid tech at SMA and we were able to resolve the issue. I
am not sure what we did but I suspect that simply rebooting the Sunny
Islands was the cure.
I post this in case any of you experience this problem and could benefit
from my experience. Also, I want to understand this better. Could it be
true that the inverters could send power to the generator? I know the
circuitry is there to sell to AC2, which is how this system would work as
a true grid-interactive system, but how did it get triggered? Was it
battery-selling to the generator? I welcome any comments.
What I am starting to think is that the Sunny Island system, like any
feature rich system, is complicated and has the potential to be less
reliable than simpler systems. On the plus side I could also think of
these systems as job security for the knowledgeable technician.
Sincerely,
William
<image002.jpg>
Lic 773985
millersolar.com
805-438-5600
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
Tump at swnl.net www.SWNL.net
Solarwinds Northernlights
Serving Mid Coast Maine & Northern California
207-832-7574 Cl. 610-517-8401
Blair "TUMP" May
******** MAINE'S CHARTER ********
NABCEP "Certified PV Installer"
******** MAINE'S CHARTER ********
Trace Xantrex "Certified" Dealer / Installer"
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140919/86a0c586/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 14092 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140919/86a0c586/attachment-0002.jpe>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: VE_Marine_generator_test_RVA_07-jan-2008.pdf
Type: application/octet-stream
Size: 3860859 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140919/86a0c586/attachment-0005.obj>
More information about the RE-wrenches
mailing list