Hi William,

The requirement for bonding on BOTH ends comes when the wire though the conduit is a GEC.  For EGC, just one end of the conduit is sufficient.

Blessings,
Kelly


~~~~~
Kelly Larson
707-223-3209

Box 504
Ukiah, CA 95482
Electrical Engineer
NABCEP Certified Solar PV Installation Professional
IREC Certified Master Trainer for Photovoltaic Installer
CA Electrical Contractor# 868189
SolarKelly.com

On Jul 14, 2014, at 3:11 PM, William Miller wrote:

> Friends:
> 
> Please help us settle a crew debate before we come to blows:  for circuits 250 volts and higher, do we need to bond EMT at both ends?  Or, if there is bonded cabinet with a concentric on one end and a solid, bonded metal cabinet on the other, do we need a bonding bushing on the concentric end?
> 
> I say a conduit needs to be bonded only on one end. My misguided employee says both ends. Both cabinets are independently bonded.
> 
> Thanks in advance. 
> 
> William
> Miller Solar
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140714/8c9b0811/attachment-0002.html>


More information about the RE-wrenches mailing list