[RE-wrenches] Concentrics at 250 volts plus

William Miller william at millersolar.com
Mon Jul 14 22:46:40 PDT 2014


Kelly:

 

Just as I suspected.  I wish you could be here to share the lunch I have
earned on my bet.

 

Thanks,

 

William

 

 

Gradient Cap_mini
Lic 773985
 <http://www.millersolar.com/> millersolar.com
805-438-5600

 

From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of Kelly Larson
Sent: Monday, July 14, 2014 10:16 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Concentrics at 250 volts plus

 

Hi William,

 

The requirement for bonding on BOTH ends comes when the wire though the
conduit is a GEC.  For EGC, just one end of the conduit is sufficient.


Blessings,

Kelly

 

 

~~~~~

Kelly Larson

707-223-3209

 

Box 504
Ukiah, CA 95482
Electrical Engineer

NABCEP Certified Solar PV Installation Professional

IREC Certified Master Trainer for Photovoltaic Installer
CA Electrical Contractor# 868189

SolarKelly.com

 

On Jul 14, 2014, at 3:11 PM, William Miller wrote:





Friends:

Please help us settle a crew debate before we come to blows:  for circuits
250 volts and higher, do we need to bond EMT at both ends?  Or, if there is
bonded cabinet with a concentric on one end and a solid, bonded metal
cabinet on the other, do we need a bonding bushing on the concentric end?

I say a conduit needs to be bonded only on one end. My misguided employee
says both ends. Both cabinets are independently bonded.

Thanks in advance. 

William
Miller Solar
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140714/15f7bc8e/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1460 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140714/15f7bc8e/attachment-0002.jpg>


More information about the RE-wrenches mailing list