A 60 amp continuously rated AC breaker is what is actually being used in
the UL listed E Panel from Midnite.
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 7/3/2014 9:01 PM, Brian Teitelbaum wrote:
>
> Mac,
>
> Be careful with breaker sizing here. The transfer switch in the SMA
> SI5048 is only rated for 56A at 120 VAC. From the SI manual:
>
> "The maximum input current allowed on the Sunny Island is 56 A. Higher
> input currents must not be connected to the Sunny Island."
>
> To protect that switch properly, you would need to use a 50A breaker
> (unless you can find a 55A breaker that fits in your AC panel). Since
> most common AC breakers are only rated for 80% duty, you would need to
> limit that 50A breaker to a continuous 40A load. That's more than the
> max output current of the Fronius 10.0-1, although it's debatable that
> the output of a PV inverter is "continuous". It certainly could be in
> some situations, especially with a tracker mount, although even with a
> fixed array, you could see max rated output for at least a couple of
> hours per day.
>
> I agree with the suggestion of putting part of the PV array on a 5kW
> Sunny Boy, or adding a second Sunny Island and using two Sunny Boy
> 5000's. Using two Islands would eliminate the need for a transformer,
> and allow for full array power during grid outages.
>
> Brian Teitelbaum
>
> AEE Solar
>
> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org
> <mailto:re-wrenches-bounces at lists.re-wrenches.org>] *On Behalf Of *Mac
> Lewis
> *Sent:* Thursday, July 03, 2014 9:34 AM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Sunny Island retrofit
>
> Hi Wrenches,
>
> Jerry, I think you are correct, sma gear all around would be best.
> This will be my recommendation but I am sensitive to this substantial
> cost.
>
> Dave, if I add the second Sunny Island, I don't think I will be
> throttled back because the transfer relays are rated for 60A. This
> should pass the full current of the output of the Fronius, which is
> 41.7A. My concern is more during backup mode, if the Sunny Islands
> could "trick" the Fronius into staying on line. I would add either
> load dump relay control or an AC interrupt relay to knock the Fronius
> off-line if the batteries were full, in addition to the frequency
> shift control that the Sunny Island offers.
>
> Thanks for the input, I'll shoot for all SMA gear.
>
> Thanks
>
> On Thu, Jul 3, 2014 at 9:23 AM, Dave Click <daveclick at fsec.ucf.edu
> <mailto:daveclick at fsec.ucf.edu>> wrote:
>
> Mac, that Island interconnects with a max 70A 1P breaker (6.7kW
> continuous), so unless they have a constant critical load draw or the
> Fronius is massively oversized, you probably don't want to AC couple
> the Fronius. The 5048 is also able to output a continuous 5000W only
> when it's cooler than 77F and it derates above that (4500W at 95F, for
> example). I don't believe its surge ratings apply to the AC2 output
> back into the utility but they probably wouldn't be enough, anyway. I
> think that whenever the Fronius output reached about 6000W, the SI
> would shift its frequency to switch the Fronius off. Cheapest may be
> along the lines of your first option-- not sure what the PV stringing
> is like but maybe you could move a string or two off the Fronius and
> put it onto a new Sunny Boy with an autoformer. Since I imagine this
> system doesn't have PV WIRE on the module leads or home runs,
> officially I'd recommend a classic Sunny Boy. Then leave the Fronius
> as-is.
>
> Unless of course the customer thought they were buying a system with
> the full 10kW supplying critical loads when the utility is down...
> then the original contractor is stuck with buying the second SI they
> should have installed in the first place.
>
> DKC
>
>
> On 2014/7/3, 10:46, Mac Lewis wrote:
>
> Hello wrenches,
>
> I wanted to run this scenario by the forum. I have spoken with
> SMA about this, but want some other opinions.
>
> We were recently contracted by a fellow solar company to do some
> warranty work for them out of town on a Sunny Island system that
> they had installed about 5 years ago. It was VERY poorly
> implemented originally and was never installed as SMA intended.
> In fact, during a small power outage, the only loads that never
> came back on after the utility was back on line were the loads in
> the critical load panel. Oops.
>
> Anyway, our job is to get it working properly for the least amount
> of cost possible. They have a Fronius IG Plus 10.0 fed into a
> 400A service panel. The Sunny Island 5048 AC Input also comes off
> of this panel and feeding a 120V only critical load panel. Please
> note that there is no solar fed into the AC output side of the
> Sunny Island, because there is not 120/240 available and thus
> there is no possible way for this system to utilize the solar
> while the grid is not present.
>
> I see two options (but there may be more): pull out Fronius, put
> in Sunny Boy inverters and an autoformer, wire properly. Another
> option is to add second Sunny Island and try to AC couple the
> Fronius with the two Sunny Islands. The second option is less
> expensive overall, but I'm hesitant to rely on AC coupling with
> the Fronius.
>
> I'd appreciate any thoughts on this.
>
> Thanks
>
>
> --
>
> Mac Lewis**
>
> "Yo solo sé que no sé nada." *-Sócrates***
>
> _______________________________________________
>
> List sponsored by Redwood Alliance
>
>
>
> List Address:RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>
>
>
> Change listserver email address & settings:
>
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>
>
> List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>
>
> List rules & etiquette:
>
> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>
>
>
> Check out or update participant bios:
>
> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
> <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
> --
>
> Mac Lewis**
>
> "Yo solo sé que no sé nada." *-Sócrates***
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140703/a6fb3b56/attachment-0002.html>
More information about the RE-wrenches
mailing list