[RE-wrenches] Combining Multiple Inverters
Dave Click
daveclick at fsec.ucf.edu
Thu Jun 26 14:20:16 PDT 2014
Corey,
The line of reasoning is faulty. It's 705.12(D)(1). Micro-inverters are
the exception because they are specially listed to share a breaker. As
for the other inverters, doubling them up on a single breaker /
disconnect probably goes against their installation instructions
[110.3(B)] and it's unlikely that you could put multiple units on a
single breaker anyway because when you take (2 inverters) x (rated
current) x (1.25) you will probably come up with a minimum breaker size
that is larger than the maximum allowed under the NRTL listing to UL 1741.
Dave
On 2014/6/26, 16:18, Corey Shalanski wrote:
> We considered the necessity to shut down individual inverters and
> determined that the added costs of an inverter output combiner panel
> were not merited. I agree that in theory it seems beneficial to be
> able to switch each inverter individually, but how often does this
> occur in practice? For the relatively infrequent cases where we need
> to return to a jobsite and shut down an inverter - for
> troubleshooting/removal/etc. - we do not mind shutting down the other
> inverters (up to a limit) for what is hopefully a short period of time.
>
> Again, this whole line of reasoning may be shown to be faulty if
> someone can directly point to the Code section that requires OCPD on
> each individual inverter.
>
> --
> Corey
> ?
>
>
> On Thu, Jun 26, 2014 at 9:20 AM,
> <re-wrenches-request at lists.re-wrenches.org
> <mailto:re-wrenches-request at lists.re-wrenches.org>> wrote:
>
>
> Message: 5
> Date: Wed, 25 Jun 2014 19:17:57 -0700
> From: William Miller <william at millersolar.com
> <mailto:william at millersolar.com>>
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org
> <mailto:re-wrenches at lists.re-wrenches.org>>
> Subject: Re: [RE-wrenches] Combining Multiple Inverters
> Message-ID: <04F4B8FD-E280-4BF2-B5A4-C2FCA8D1C7A6 at millersolar.com
> <mailto:04F4B8FD-E280-4BF2-B5A4-C2FCA8D1C7A6 at millersolar.com>>
> Content-Type: text/plain; charset="utf-8"
>
> Not allowed. You need a dedicated OCPD. Plus seems like a really
> bad idea. How do you shut down just one inverter?
>
>
>
> Miller Solar
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140626/76d46429/attachment-0002.html>
More information about the RE-wrenches
mailing list