<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    Corey,<br>
    <br>
    The line of reasoning is faulty. It's 705.12(D)(1). Micro-inverters
    are the exception because they are specially listed to share a
    breaker. As for the other inverters, doubling them up on a single
    breaker / disconnect probably goes against their installation
    instructions [110.3(B)] and it's unlikely that you could put
    multiple units on a single breaker anyway because when you take (2
    inverters) x (rated current) x (1.25) you will probably come up with
    a minimum breaker size that is larger than the maximum allowed under
    the NRTL listing to UL 1741.<br>
    <br>
    Dave<br>
    <br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 2014/6/26, 16:18, Corey Shalanski
      wrote:<br>
    </div>
    <blockquote
cite="mid:CA+SmqZ29-HUrwOjJKtTArB3nN8xQzex9PtYe05FBc2UKJodPrA@mail.gmail.com"
      type="cite">
      <div dir="ltr">We considered the necessity to shut down individual
        inverters and determined that the added costs of an inverter
        output combiner panel were not merited. I agree that in theory
        it seems beneficial to be able to switch each inverter
        individually, but how often does this occur in practice? For the
        relatively infrequent cases where we need to return to a jobsite
        and shut down an inverter - for troubleshooting/removal/etc. -
        we do not mind shutting down the other inverters (up to a limit)
        for what is hopefully a short period of time.
        <div>
          <br>
        </div>
        <div>Again, this whole line of reasoning may be shown to be
          faulty if someone can directly point to the Code section that
          requires OCPD on each individual inverter.</div>
        <div><br>
        </div>
        <div>--</div>
        <div>Corey<br>
          <div hspace="streak-pt-mark" style="max-height:1px"><img
              moz-do-not-send="true" style="width:0px; max-height:0px;"
src="https://mailfoogae.appspot.com/t?sender=aY3NoYWxhbnNraUBqb3VsZS1lbmVyZ3kuY29t&type=zerocontent&guid=59f6d492-9013-469d-af5f-e28b249c1b4b"><font
              color="#ffffff" size="1">ᐧ</font></div>
          <div class="gmail_extra"><br>
            <br>
            <div class="gmail_quote">On Thu, Jun 26, 2014 at 9:20 AM, <span
                dir="ltr"><<a moz-do-not-send="true"
                  href="mailto:re-wrenches-request@lists.re-wrenches.org"
                  target="_blank">re-wrenches-request@lists.re-wrenches.org</a>></span>
              wrote:<br>
              <blockquote class="gmail_quote" style="margin:0 0 0
                .8ex;border-left:1px #ccc solid;padding-left:1ex"><br>
                Message: 5<br>
                Date: Wed, 25 Jun 2014 19:17:57 -0700<br>
                From: William Miller <<a moz-do-not-send="true"
                  href="mailto:william@millersolar.com">william@millersolar.com</a>><br>
                To: RE-wrenches <<a moz-do-not-send="true"
                  href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>><br>
                Subject: Re: [RE-wrenches] Combining Multiple Inverters<br>
                Message-ID: <<a moz-do-not-send="true"
                  href="mailto:04F4B8FD-E280-4BF2-B5A4-C2FCA8D1C7A6@millersolar.com">04F4B8FD-E280-4BF2-B5A4-C2FCA8D1C7A6@millersolar.com</a>><br>
                Content-Type: text/plain; charset="utf-8"<br>
                <br>
                Not allowed. You need a dedicated OCPD. Plus seems like
                a really bad idea.  How do you shut down just one
                inverter?<br>
                <br>
                <br>
                <br>
                Miller Solar</blockquote>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>