Jason Szumlanski jason at fafcosolar.com
Thu Jun 26 11:12:47 PDT 2014


Yeah, 1k/2k wire shows a diameter of 0.26" on the spec sheet, or 0.053093
in^2.

Jason Szumlanski

​Fafco Solar​




On Thu, Jun 26, 2014 at 2:06 PM, Kirk <kirk at vtsolar.com> wrote:

> Nice calculator. RHH may be equivalent to 600 volt pv wire, but 1k/2k pv
> wire is thicker.
>
> Kirk Herander
> VSE
>
> On Jun 26, 2014, at 1:49 PM, Jason Szumlanski <jason at fafcosolar.com>
> wrote:
>
> I use this site when I need a quick answer. Use RHH (covered) with one
> conductor. You get the same answer.
>
> http://www.electrician2.com/calculators/rf_calculator.html
>
>
> Jason Szumlanski
>
> ​Fafco Solar​
>
>
> On Thu, Jun 26, 2014 at 1:46 PM, Jason Szumlanski <jason at fafcosolar.com>
> wrote:
>
>> 0.0437435 per this attached spec sheet for 600V.
>>
>>
>>  Jason Szumlanski
>>
>>
>> On Thu, Jun 26, 2014 at 1:15 PM, Kirk <kirk at vtsolar.com> wrote:
>>
>>> Hi folks,
>>> What is the proper approximate in2  area to use for #10 1kva/2kva  pv
>>> wire for calculating conduit fill? I'm on a job site and don't have the
>>> specs with me. Thanks.
>>>
>>> Kirk Herander
>>> VSE
>>>
>>>
>>