Bill Brooks billbrooks7 at yahoo.com
Fri Jun 27 17:20:37 PDT 2014


Kirk,

 

The tables in Appendix C are just for reference. They are not part of the Code. The only real part of the code is in chapter 9:

 

Table 1 Percent of Cross Section of Conduit and Tubing for

Conductors and Cables

Number of Conductors      and/or Cables Cross-Sectional Area (%)

1                                               53

2                                               31

Over 2                                      40

 

 

Many conductors do not have standard cross-sectional areas.


Bill.

 

 

From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jason Szumlanski
Sent: Thursday, June 26, 2014 11:13 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Pv wire

 

Yeah, 1k/2k wire shows a diameter of 0.26" on the spec sheet, or 0.053093 in^2.

 

Jason Szumlanski

​Fafco Solar​


  <https://wisestamp.appspot.com/pixview.gif?p=chrome&v=3.42.0&t=1403806149111&u=dedcb4cd140ce271> 

  <http://ws-stats.appspot.com/ga/pixel.png?yes__count=true&e=legacy_impression> 

 

On Thu, Jun 26, 2014 at 2:06 PM, Kirk <kirk at vtsolar.com <mailto:kirk at vtsolar.com> > wrote:

Nice calculator. RHH may be equivalent to 600 volt pv wire, but 1k/2k pv wire is thicker. 

Kirk Herander

VSE


On Jun 26, 2014, at 1:49 PM, Jason Szumlanski <jason at fafcosolar.com <mailto:jason at fafcosolar.com> > wrote:

I use this site when I need a quick answer. Use RHH (covered) with one conductor. You get the same answer.

 

http://www.electrician2.com/calculators/rf_calculator.html

 

Jason Szumlanski

​Fafco Solar​

 

 

On Thu, Jun 26, 2014 at 1:46 PM, Jason Szumlanski <jason at fafcosolar.com <mailto:jason at fafcosolar.com> > wrote:

0.0437435 per this attached spec sheet for 600V.

 

Jason Szumlanski

  <http://ws-stats.appspot.com/ga/pixel.png?yes__count=true+&e=legacy_impression> 

 

On Thu, Jun 26, 2014 at 1:15 PM, Kirk <kirk at vtsolar.com <mailto:kirk at vtsolar.com> > wrote:

Hi folks,
What is the proper approximate in2  area to use for #10 1kva/2kva  pv wire for calculating conduit fill? I'm on a job site and don't have the specs with me. Thanks.

Kirk Herander
VSE

 

 

___



---
This email is free from viruses and malware because avast! Antivirus protection is active.
http://www.avast.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140627/1f3c3dce/attachment-0002.html>


More information about the RE-wrenches mailing list