Nice calculator. RHH may be equivalent to 600 volt pv wire, but 1k/2k pv wire is thicker. 

Kirk Herander
VSE

> On Jun 26, 2014, at 1:49 PM, Jason Szumlanski <jason at fafcosolar.com> wrote:
> 
> I use this site when I need a quick answer. Use RHH (covered) with one conductor. You get the same answer.
> 
> http://www.electrician2.com/calculators/rf_calculator.html
> 
> 
> Jason Szumlanski
> ​Fafco Solar​
> 
>> On Thu, Jun 26, 2014 at 1:46 PM, Jason Szumlanski <jason at fafcosolar.com> wrote:
>> 0.0437435 per this attached spec sheet for 600V.
>> 
>> 
>> Jason Szumlanski
>> 
>> 
>> 
>>> On Thu, Jun 26, 2014 at 1:15 PM, Kirk <kirk at vtsolar.com> wrote:
>>> Hi folks,
>>> What is the proper approximate in2  area to use for #10 1kva/2kva  pv wire for calculating conduit fill? I'm on a job site and don't have the specs with me. Thanks.
>>> 
>>> Kirk Herander
>>> VSE
> 