[RE-wrenches] 208 3 phase Off Grid Inverter
Ray Walters
ray at solarray.com
Wed Mar 26 08:29:56 PDT 2014
Its Mexico, so its 60 Hz, 3 phase 120/ 208. I had originally
considered the Radians for this project, until I went down and
determined the actual voltage.
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 3/26/2014 7:31 AM, Phil Undercuffler wrote:
> You mentioned this is out of the country -- is it 230v line to
> neutral, or 120/208? OutBack's export Radian can do three phase, up
> to 72kW continuous.
>
> HTH,
>
> Phil
>
>
>
>
> On Tuesday, March 25, 2014, Ray Walters <ray at solarray.com
> <mailto:ray at solarray.com>> wrote:
>
> OK everyone is steering me towards the Sunny Island. I can
> probably justify the inverter cost difference to the customer,
> then I found the SMA Multicluster Box for the SI. It seems like a
> glorified AC Combiner and transfer switch box, but it retails for
> over $20K! Yikes.
> Do we have to use that for a 3 phase install, or are there much
> lower cost alternatives. This is out of the country and does not
> need to be NEC2014 compliant. (maybe NEC 1956 compliant would be
> about in keeping with the rest of the wiring.......) This would
> be a budget buster for sure.
>
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer,
> Licensed Master Electrician
> Solar Design Engineer
> 303 505-8760
>
> On 3/25/2014 4:21 PM, Kevin Pegg wrote:
>
> Hi Ray,
>
> I have several 3-phase off-grid inverter/battery/generator
> systems out there.
>
> - SMA Sunny Island is the best. Can scale to at least 180 kW,
> maybe more. Reliable & very solid. I have several sites going
> over 2 years without a single second of power outage.
> - Xantrex XW. It can work in a 3-ph config, but it's not as
> stable system. We have taken to preventatively rebooting the
> systems every 4 months and that helps a lot - at least the
> outage can be planned and on our terms.
> - Outback has had so many power quality nightmares I won't go
> there anymore.
> - I believe Magnum has a 3-ph option but haven't installed one
> yet.
>
> SMA inverters are more expensive. And they work very well.
> They also have a very good battery charging algorithm and
> integral gen start control.
>
> Kevin
>
> -----Original Message-----
> From: re-wrenches-bounces at lists.re-wrenches.org
> [mailto:re-wrenches-bounces at lists.re-wrenches.org]On Behalf Of Ray
> Walters
> Sent: March 24, 2014 6:44 PM
> To: RE-wrenches
> Subject: [RE-wrenches] 208 3 phase Off Grid Inverter
>
>
> Hi All;
>
> I'm exploring options for an off grid project with an existing
> 30 Kw
> Kohler wired for 208 vac 3 phase. The generator runs some 8
> hp air
> compressors, so rewiring it is not an option. We're primarily
> interested in reducing gen run time from the current
> situation: 14 hrs/ day.
> So far, only the Outback VFX inverters seem capable of being
> wired in
> 208, 3 phase, but according to the manual they can only be
> stacked 1
> inverter per leg. This limits the system to only 3 inverters
> total, or
> 10.8 kW. I would like expandability beyond this.
> 1) are there any other inverters available that I'm over looking?
> 2) Should I consider a transformer to convert from 208
> vac/3phase to 240
> vac/ singe phase?
>
> We're not going to even try to run the compressors, just the other
> single phase loads, mostly 120 vac, but we have a couple of
> small air
> conditioners, that are currently running on 208 single phase.
> I believe
> they would run fine on 240 vac, as they have a name plate
> rating at 230 vac.
> 3) We may possibly run 2 separate 3 inverter stacks and only tie
> together at the battery, but otherwise they would not be
> connected. This
> seems inefficient, and would require some load balancing of
> the various
> inverters.
>
> All help and discussion is greatly appreciated as always,
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>
>
> Check out participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140326/e4baf43d/attachment-0004.html>
More information about the RE-wrenches
mailing list