[RE-wrenches] 208 3 phase Off Grid Inverter

Phil Undercuffler solarphil at gmail.com
Wed Mar 26 06:31:46 PDT 2014


You mentioned this is out of the country -- is it 230v line to neutral, or
120/208?  OutBack's export Radian can do three phase, up to 72kW
continuous.

HTH,

Phil




On Tuesday, March 25, 2014, Ray Walters <ray at solarray.com> wrote:

> OK everyone is steering me towards the Sunny Island.   I can probably
> justify the inverter cost difference to the customer, then I found the SMA
> Multicluster Box for the SI.  It seems like a glorified AC Combiner and
> transfer switch box, but it retails for over $20K! Yikes.
> Do we have to use that for a 3 phase install, or are there much lower cost
> alternatives.  This is out of the country and does not need to be NEC2014
> compliant.  (maybe NEC 1956 compliant would be about in keeping with the
> rest of the wiring.......)  This would be a budget buster for sure.
>
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer,
> Licensed Master Electrician
> Solar Design Engineer
> 303 505-8760
>
> On 3/25/2014 4:21 PM, Kevin Pegg wrote:
>
>> Hi Ray,
>>
>> I have several 3-phase off-grid inverter/battery/generator systems out
>> there.
>>
>> - SMA Sunny Island is the best. Can scale to at least 180 kW, maybe more.
>> Reliable & very solid. I have several sites going over 2 years without a
>> single second of power outage.
>> - Xantrex XW. It can work in a 3-ph config, but it's not as stable
>> system. We have taken to preventatively rebooting the systems every 4
>> months and that helps a lot - at least the outage can be planned and on our
>> terms.
>> - Outback has had so many power quality nightmares I won't go there
>> anymore.
>> - I believe Magnum has a 3-ph option but haven't installed one yet.
>>
>> SMA inverters are more expensive. And they work very well. They also have
>> a very good battery charging algorithm and integral gen start control.
>>
>> Kevin
>>
>> -----Original Message-----
>> From: re-wrenches-bounces at lists.re-wrenches.org
>> [mailto:re-wrenches-bounces at lists.re-wrenches.org]On Behalf Of Ray
>> Walters
>> Sent: March 24, 2014 6:44 PM
>> To: RE-wrenches
>> Subject: [RE-wrenches] 208 3 phase Off Grid Inverter
>>
>>
>> Hi All;
>>
>> I'm exploring options for an off grid project with an existing 30 Kw
>> Kohler wired for 208 vac 3 phase.  The generator runs some 8 hp air
>> compressors, so rewiring it is not an option.  We're primarily
>> interested in reducing gen run time from the current situation: 14 hrs/
>> day.
>> So far, only the Outback VFX inverters seem capable of being wired in
>> 208, 3 phase, but according to the manual they can only be stacked 1
>> inverter per leg. This limits the system to only 3 inverters total, or
>> 10.8 kW.  I would like expandability beyond this.
>> 1) are there any other inverters available that I'm over looking?
>> 2) Should I consider a transformer to convert from 208 vac/3phase to 240
>> vac/ singe phase?
>>
>> We're not going to even try to run the compressors, just the other
>> single phase loads, mostly 120 vac, but we have a couple of small air
>> conditioners, that are currently running on 208 single phase.  I believe
>> they would run fine on 240 vac, as they have a name plate rating at 230
>> vac.
>> 3) We may possibly run 2 separate 3 inverter stacks and only tie
>> together at the battery, but otherwise they would not be connected. This
>> seems inefficient, and would require some load balancing of the various
>> inverters.
>>
>> All help and discussion is greatly appreciated as always,
>>
>>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-
> wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140326/c85b7c37/attachment-0003.html>


More information about the RE-wrenches mailing list