You mentioned this is out of the country -- is it 230v line to neutral, or 120/208?  OutBack's export Radian can do three phase, up to 72kW continuous. <div><br></div><div>HTH,<br><div><br></div><div>Phil<br><div><br></div>
<div><br></div><div><br><br>On Tuesday, March 25, 2014, Ray Walters <<a href="mailto:ray@solarray.com">ray@solarray.com</a>> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
OK everyone is steering me towards the Sunny Island.   I can probably justify the inverter cost difference to the customer, then I found the SMA Multicluster Box for the SI.  It seems like a glorified AC Combiner and transfer switch box, but it retails for over $20K! Yikes.<br>

Do we have to use that for a 3 phase install, or are there much lower cost alternatives.  This is out of the country and does not need to be NEC2014 compliant.  (maybe NEC 1956 compliant would be about in keeping with the rest of the wiring.......)  This would be a budget buster for sure.<br>

<br>
R.Ray Walters<br>
CTO, Solarray, Inc<br>
Nabcep Certified PV Installer,<br>
Licensed Master Electrician<br>
Solar Design Engineer<br>
303 505-8760<br>
<br>
On 3/25/2014 4:21 PM, Kevin Pegg wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
Hi Ray,<br>
<br>
I have several 3-phase off-grid inverter/battery/generator systems out there.<br>
<br>
- SMA Sunny Island is the best. Can scale to at least 180 kW, maybe more. Reliable & very solid. I have several sites going over 2 years without a single second of power outage.<br>
- Xantrex XW. It can work in a 3-ph config, but it's not as stable system. We have taken to preventatively rebooting the systems every 4 months and that helps a lot - at least the outage can be planned and on our terms.<br>

- Outback has had so many power quality nightmares I won't go there anymore.<br>
- I believe Magnum has a 3-ph option but haven't installed one yet.<br>
<br>
SMA inverters are more expensive. And they work very well. They also have a very good battery charging algorithm and integral gen start control.<br>
<br>
Kevin<br>
<br>
-----Original Message-----<br>
From: <a>re-wrenches-bounces@lists.re-wrenches.org</a><br>
[mailto:<a>re-wrenches-bounces@lists.re-wrenches.org</a>]On Behalf Of Ray<br>
Walters<br>
Sent: March 24, 2014 6:44 PM<br>
To: RE-wrenches<br>
Subject: [RE-wrenches] 208 3 phase Off Grid Inverter<br>
<br>
<br>
Hi All;<br>
<br>
I'm exploring options for an off grid project with an existing 30 Kw<br>
Kohler wired for 208 vac 3 phase.  The generator runs some 8 hp air<br>
compressors, so rewiring it is not an option.  We're primarily<br>
interested in reducing gen run time from the current situation: 14 hrs/ day.<br>
So far, only the Outback VFX inverters seem capable of being wired in<br>
208, 3 phase, but according to the manual they can only be stacked 1<br>
inverter per leg. This limits the system to only 3 inverters total, or<br>
10.8 kW.  I would like expandability beyond this.<br>
1) are there any other inverters available that I'm over looking?<br>
2) Should I consider a transformer to convert from 208 vac/3phase to 240<br>
vac/ singe phase?<br>
<br>
We're not going to even try to run the compressors, just the other<br>
single phase loads, mostly 120 vac, but we have a couple of small air<br>
conditioners, that are currently running on 208 single phase.  I believe<br>
they would run fine on 240 vac, as they have a name plate rating at 230 vac.<br>
3) We may possibly run 2 separate 3 inverter stacks and only tie<br>
together at the battery, but otherwise they would not be connected. This<br>
seems inefficient, and would require some load balancing of the various<br>
inverters.<br>
<br>
All help and discussion is greatly appreciated as always,<br>
<br>
</blockquote>
<br>
______________________________<u></u>_________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a>RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/<u></u>options.cgi/re-wrenches-re-<u></u>wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/<u></u>pipermail/re-wrenches-re-<u></u>wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.<u></u>htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote></div></div></div>