Kirk Herander kirk at vtsolar.com
Thu Mar 6 07:47:57 PST 2014


Changes to
<http://www.google.com/url?sa=t&rct=j&q=&esrc=s&source=web&cd=3&cad=rja&uact
=8&ved=0CEoQFjAC&url=http%3A%2F%2Fwww.slideshare.net%2Fsolpowerpeople%2Finte
rconnection-rule&ei=FZcYU5e_LsSi0QH5yICQCQ&usg=AFQjCNGypW0SbS6-POHt4d82Sxc--
kZ0ig&sig2=Kz2661LzDghXtx9GwuhOfw&bvm=bv.62577051,d.dmQ> 2014 NEC
Interconnection Rule 705.12

Here's a link to a powerpoint (slideshare.net) by Richard Stovall which
clarifies 705.12 using some excellent illustrations. Maybe some have seen it
already. Works for me.

Contact me off-list if you'd like a pdf version.

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified Inaugural Certificant

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Brian
Mehalic
Sent: Wednesday, March 05, 2014 10:02 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] conductors and the 120% rule

 

A very clarifying change is what I'd call it! 

 

First off, rather than being based on the actual breaker size on the
inverter output circuit, calcs are instead based on 125% of the inverter
rated output current.

 

705.12(D)(2)(1) addresses "Feeders" - but only applies when the inverter
output circuit connection is made somewhere other than the opposite end of
the feeder from the utility supply.  This addresses concerns about whether
the feeder conductor needs to be larger due to the presence of the
additional source of supply, and so long as the inverter isn't connected to
the feeder in the middle of it then the existing conductor size should be
okay (because if it is at the opposite end of the feeder than there is
nowhere where the utility and inverter current will be additive).

 

705.12(D)(2)(3) addresses "Busbars" and allows several options, including
the familiar "120% rule" as you stated in your original post.  Also check
out 705.12(D)(2)(3)(c) - depending on the load breakers in the subpanel, the
120% rule may not even need to be used (if the sum of the inverter and load
breakers is less than or equal to the busbar rating).

 

And remember, even if your AHJ hasn't adopted 2014 yet it is worth having a
conversation with them to see if they'll allow you to design the system
based on the new Code - after all, in a certain sense, the 2014 NEC is what
"they" meant the 2011 NEC to say!

 

Cheers,




 

Brian Mehalic 
NABCEP Certified Solar PV Installation ProfessionalT R031508-59

IREC ISPQ Certified Affiliated Instructor/PV US-0132

 

PV Curriculum Developer and Instructor

Solar Energy International
http://www.solarenergy.org

 

On Tue, Mar 4, 2014 at 5:21 PM, Kirk <kirk at vtsolar.com> wrote:

Is this a code change in 2014 vs 2011 or merely a clarification? Vt has not
adopted 2014 yet. What was the original rationale for the 120% rule to apply
to conductors in addition to a panel bus? 

Kirk Herander

VSE


On Mar 4, 2014, at 6:20 PM, Brian Mehalic <brian at solarenergy.org> wrote:

If the subpanel is at the end if the feeder, and there are no taps in
between the main and the sub then I don't see any reason that the conductors
need to be any larger than 200 A as there is no where on the feeder
conductors where grid and PV current will be additive. 

 

The changes in 705.12 in 2014 address this in large part. 

Brian


On Mar 4, 2014, at 2:41 PM, "Kirk Herander" <kirk at vtsolar.com> wrote:

Solaredge 20 kw, 480 3-phase. Good point, but that may be irrelevant. The
feed-in subpanel is also powering unrelated loads, which use the neutral as
a conductor from the main panel. So 4 conductors from the main.

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified Inaugural Certificant

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Allen
Frishman
Sent: Tuesday, March 04, 2014 4:32 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] conductors and the 120% rule

 

what inverter(s) are you using?    In many cases the Neutral is not
considered a Current Carying Conductor by the Manufacturer and therefore you
only have 3 CCC.

Al Frishman
AeonSolar

(917) 699-6641 <tel:%28917%29%20699-6641>  - cell
(888) 460-2867 <tel:%28888%29%20460-2867> 
www.aeonsolar.com <http://www.aeonsolar.com/> 

 

On Mar 4, 2014, at 4:20 PM, Kirk Herander wrote:

 

Approx.. 50 - 60ft.

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified Inaugural Certificant

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Ray Walters
Sent: Tuesday, March 04, 2014 4:05 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] conductors and the 120% rule

 

What is the length of the conduit to the subpanel? That will determine
whether to apply the derates.



R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760 <tel:303%20505-8760> 

On 3/4/2014 1:34 PM, Kirk Herander wrote:

Whether or not a further derate has to be applied is the killer here, as I
am working with existing panels and conductors. In an old Code Corner(HP140)
J. Wiles goes through a similar scenario and calls out the allowable current
rating and conductor in 310.15, but makes no mention of applying additional
derate factors. The .8 derate for 4-6 conductors(l1,l2,l3, & n) will put the
existing 4/0 cable between feed-in and main panel at 208 amps, less than the
allowable 217. I'd hate to need to upsize the wire to 250 mcm.

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified Inaugural Certificant

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Tuesday, March 04, 2014 2:57 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] conductors and the 120% rule

 

Both the bus and conductors need to be rated for 217 amps minimum. As you
mentioned, the bus is not a problem. The way I interpret it, the conductor
size required would be after derate factors are applied. The rating of the
conductor is ultimately dependent on the derate factors.

 

If you can locate your subpanel adjacent to the main distribution panel, you
may be able to use Exception #3 to 310.15(B)(2) by connecting the panels
with a short nipple. I assume you are just looking at a number of conductor
derate and not an ambient temperature derate.

 

Jason Szumlanski

Fafco Solar


 

<image001.jpg>

 

On Tue, Mar 4, 2014 at 12:05 PM, Kirk Herander <kirk at vtsolar.com> wrote:

Hello,

I have a 225 amp 3-phase main lug sub-panel protected by a 200 amp breaker.
My inverter breaker feeding the sub panel is 60 amps. So 225 a bus x 1.2 =
270 amps. That's less than the sum of the two breakers of 260 amps, so no
issue there. The conductors between sub and main panel have to be rated for
at least 260/1.2 = 217 amps, correct? Is this 217 amps before or after
derating the conductor?

 

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified Inaugural Certificant

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

 






_______________________________________________
List sponsored by Home Power magazine
 
List Address: RE-wrenches at lists.re-wrenches.org
 
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
 
Check out participant bios:
www.members.re-wrenches.org
 

 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140306/1764b39c/attachment-0004.html>


More information about the RE-wrenches mailing list