On 1/23/2014 4:17 PM, Dan Fink wrote:
> Thanks for the correction on that sedona fire Bill; I had only seen 
> the incorrect fire dept report.
> I wish there was a clearinghouse for information on RE incidents and 
> close calls as they are all teachable moments for both RE 
> professionals and firefighters.
>
> I ditto the need for more NEC guidance on battery banks. In my 
> firefighting career, I've been at about a dozen structure fires 
> involving RE equipment. Only 4 were actually caused by the RE 
> equipment. *All* of those originated in or near the battery bank. 1 
> internal battery short circuit, 1 mouse chew inside battery box, and 2 
> bad connection when charging with a generator.
>
> I'd like to get involved, Bill....I have lots to say about wooden 
> battery boxes, parallel fusing, signage, and more. What are the first 
> steps for getting involved?
>
>
> Dan Fink,
> Executive Director;
> Otherpower
> Buckville Energy Consulting
> Buckville Publications LLC
> NABCEP / IREC accredited Continuing Education Providers
> 970.672.4342
>
>
>
> On Thu, Jan 23, 2014 at 12:23 PM, Bill Brooks <billbrooks7 at yahoo.com 
> <mailto:billbrooks7 at yahoo.com>> wrote:
>
>     Jeffrey and Ray,
>
>     Batteries can off-gas hydrogen-sulfide gas when under heavy charge
>     or overcharge. It is the nasty rotten egg smelling gas. Definitely
>     not to be inhaled since when it hits your lungs it turns back into
>     sulfuric acid.
>
>     To address Ray's point, the new 690.12 regulation that has been
>     getting a lot of air time on this list does, in fact, address
>     battery circuits for PV systems. Any circuit that is part of a PV
>     system inside a building within 5' must be controlled to 30V,
>     240VA within 10 seconds. This includes all the ac output
>     conductors from a backup PV inverter and the battery inverter
>     input circuit as well. This provision matches the new requirement
>     for battery systems in 690.71(H) that requires "A disconnecting
>     means and overcurrent protection shall be provided at the energy
>     storage device end of the circuit. Fused disconnecting means or
>     circuit breakers shall be permitted to be used." Ideally we try to
>     keep our battery conductors to 5' or less and that means that no
>     additional disconnecting means would be necessary according to the
>     new 690.71(H). If we have to go longer than 5' and the conductors
>     are inside the building, a rapid shutdown capability would need to
>     be on that circuit and it would need to have a disconnecting means
>     and overcurrent protection. The best way to meet this requirement
>     would probably be to have a shunt-trip breaker, similar to what
>     Midnite Solar provides with their birdhouse setup.
>
>     There are definitely much more discussion going on in the NEC
>     about energy storage now than ever before. This next code cycle
>     will be very busy on the subject. It is likely that article 480
>     will soon be turned into "Energy Storage" or a new article in
>     Chapter 6 or 7 will cover "Energy Storage Systems." It was
>     proposed last cycle and failed, but this time there is much more
>     interest in the subject. The solar industry needs to be involved,
>     so it sounds like this is your year for both of you to get involved.
>
>     Bill.
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140123/79b021c7/attachment-0004.html>


More information about the RE-wrenches mailing list