There are good reasons to want to put AC 
combiners under modules, but some reasons not to 
want to. An AC breaker is far more likely to trip 
than a DC string fuse, due to the surge 
availability. As a PV system is designed to last 
a minimum of 25 years, the installer might not be 
the one to sort out problems decades down the line.

A strategy I prefer would be to use a SolaDeck as 
a junction box. Run small wires to a convenient AC combiner location.


At 12:43 PM 4/29/2014, you wrote:
>Dave
>
>I agree, in the case of microinverters, you 
>already have a main PV System disconnect at the 
>Load Panel to shut down the system that is 
>readily accesible.  I would consider the 
>disconnect on the roof as a supplemental 
>disconnect for the purposes of maintenance by 
>authorized personal that only needs to be accessible.
>
>Bill
>
>
>On Tue, Apr 29, 2014 at 8:44 AM, Dave Click 
><<mailto:daveclick at fsec.ucf.edu>daveclick at fsec.ucf.edu> wrote:
>I think 240.24(A)(4) allows the installation of 
>the inverter OCPDs in the SolaDeck hidden under a module.
>
>240.24 Location in or on Premises.
>(A) Accessibility. Overcurrent devices shall be 
>readily accessible and shall be installed so 
>that the center of the grip of the operating 
>handle of the switch or circuit breaker, when in 
>its highest position, is not more than 2.0 m (6 
>ft 7 in.) above the floor or working platform, 
>unless one of the following applies:
>...
>(4) For overcurrent devices adjacent to 
>utilization equipment that they supply, access 
>shall be permitted to be by portable means.
>
>
>And if panelboards / fused safety switches are 
>allowed to have screwed-down covers over the 
>OCPDs, I'd think that installing a removable 
>module over these OCPDs would meet NEC. I guess 
>an AHJ could argue that this requires TWO covers 
>be removed, unlike a panelboard or a switch.
>
>DKC
>
>
>On 2014/4/29, 11:15, Jason Szumlanski wrote:
>>690.9(D) is not applicable to the original 
>>discussion because we were talking about an 
>>Inverter output circuit, not a PV Source or Output circuit.
>>
>>690.34 may apply if you call a SolaDeck with 
>>breakers a junction box, but I can see that 
>>being a stretch in the mind of many.
>>
>>My and Ray's question about the screws on the 
>>SolaDeck cover itself requiring a tool to 
>>render it accessible is still an issue if the 
>>breakers themselves need to be "readily 
>>accessible," but that would also apply to a 
>>Midnite MNPV, which also has a cover with a screw.
>>
>>
>>Jason Szumlanski
>>
>>On 4/28/2014 5:57 PM, Bill Brooks wrote:
>>>
>>>Read 690.9(D) and 690.34. Not sure where this 
>>>“hysteria­run for the border” sentiment is coming from.
>>>
>>>
>>>
>>>690.9(D) Photovoltaic Source and Output Circuits. Listed PV
>>>
>>>overcurrent devices shall be required to provide overcurrent
>>>
>>>protection in PV source and output circuits. The overcurrent
>>>
>>>devices shall be accessible but shall not be required to
>>>
>>>be readily accessible.
>>>
>>>
>>>
>>>690.34 Access to Boxes. Junction, pull, and outlet boxes
>>>
>>>located behind modules or panels shall be so installed that
>>>
>>>the wiring contained in them can be rendered accessible
>>>
>>>directly or by displacement of a module(s) or panel(s) secured
>>>
>>>by removable fasteners and connected by a flexible
>>>
>>>wiring system.
>>>
>>>
>>>
>>>This is not a change. Please help me understand the concern.
>>>
>>>
>>>
>>>Bill Brooks.
>>>
>>>
>>>
>>>
>>>
>>>From: 
>>><mailto:re-wrenches-bounces at lists.re-wrenches.org>re-wrenches-bounces at lists.re-wrenches.org 
>>>[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Ray Walters
>>>Sent: Monday, April 28, 2014 2:23 PM
>>>To: RE-wrenches
>>>Subject: Re: [RE-wrenches] (no subject)
>>>
>>>
>>>
>>>Interesting so does "require a tool" include 
>>>taking a screw off the cover plate of the combiner box, too?
>>>What a game changer.  I'm going to Mexico for 
>>>my next project; I'll actually enjoy even more 
>>>being the sole AHJ on the project.
>>>
>>>
>>>R.Ray Walters
>>>CTO, Solarray, Inc
>>>Nabcep Certified PV Installer,
>>>Licensed Master Electrician
>>>Solar Design Engineer
>>><tel:303%20505-8760>303 505-8760
>>>On 4/28/2014 2:52 PM, Michael Morningstar wrote:
>>>
>>>Readily accessible is now defined in the 2014 
>>>NEC. Installing OCPD’s underneath a module is 
>>>a major faux paux, and I can’t imagine any AHJ 
>>>thinking otherwise. Having to remove a module 
>>>in order to reset a breaker, what a drag.
>>>
>>>
>>>
>>>"Capable of being reached quickly for 
>>>operation, renewal or inspection without 
>>>requiring those concerned to use a tool, to 
>>>climb over, remove obstacle or other.”
>>>
>>>
>>>
>>>Michael
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>On Apr 28, 2014, at 10:29 AM, William Miller 
>>><<mailto:william at millersolar.com>william at millersolar.com> wrote:
>>>
>>>
>>>
>>>You call it a solar panel, I call it a glass j-box cover plate.
>>>
>>>William
>>>
>>>Miller Solar
>>>
>>>
>>>On Apr 28, 2014, at 9:21 AM, Jason Szumlanski 
>>><<mailto:jason at fafcosolar.com>jason at fafcosolar.com> wrote:
>>>
>>>If that is the interpretation,
>>>I don't see how the breakers are "readily accessible" in a SolaDeck
>>>mounted anywhere, regardless of whether it is under a module. It
>>>requires removal of four screws (using a tool) to access the breakers
>>>inside the enclosure. It's all up to the AHJ. It has not been an issue
>>>locally here. I can see how other jurisdictions may not
>>>concur.
>>
>>
>>_______________________________________________
>>List sponsored by Home Power magazine
>>
>>List Address: 
>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>
>>Change email address & settings:
>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches..org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive: 
>><http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>>List rules & etiquette:
>><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>>
>>Check out participant bios:
>><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>>
>>
>>
>>
>>
>>
>>_______________________________________________
>>
>>List sponsored by Home Power magazine
>>
>>
>>List Address: 
>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>
>>
>>Change email address & settings:
>>
>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>
>>List-Archive: 
>><http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>>
>>List rules & etiquette:
>>
>><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>>
>>
>>Check out participant bios:
>>
>><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>>
>
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: 
><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>
>Change email address & settings:
><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
><http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>
>
>
>
>
>--
>William Hoffer
>161 SE Fourth Ave
>P.O. Box 1823
>White Salmon, WA 98672-1823
><mailto:bhoffer at sunergyengineeringservices.com>sunengser at gmail.com
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140430/0f2ebf9c/attachment-0003.html>


More information about the RE-wrenches mailing list