[RE-wrenches] Article 690, or The Haves Vs. Have Nots

Jason Szumlanski jason at fafcosolar.com
Tue Apr 29 08:15:45 PDT 2014


690.9(D) is not applicable to the original discussion because we were
talking about an Inverter output circuit, not a PV Source or Output circuit..

690.34 may apply if you call a SolaDeck with breakers a junction box, but I
can see that being a stretch in the mind of many.

My and Ray's question about the screws on the SolaDeck cover itself
requiring a tool to render it accessible is still an issue if the breakers
themselves need to be "readily accessible," but that would also apply to a
Midnite MNPV, which also has a cover with a screw.


Jason Szumlanski

>
> On 4/28/2014 5:57 PM, Bill Brooks wrote:
>
>  Read 690.9(D) and 690.34. Not sure where this “hysteria—run for the
> border” sentiment is coming from.
>
>
>
> *690.9(D) Photovoltaic Source and Output Circuits. *Listed PV
>
> overcurrent devices shall be required to provide overcurrent
>
> protection in PV source and output circuits. The overcurrent
>
> devices shall be accessible but shall not be required to
>
> be readily accessible.
>
>
>
> *690.34 Access to Boxes. *Junction, pull, and outlet boxes
>
> located behind modules or panels shall be so installed that
>
> the wiring contained in them can be rendered accessible
>
> directly or by displacement of a module(s) or panel(s) secured
>
> by removable fasteners and connected by a flexible
>
> wiring system.
>
>
>
> This is not a change. Please help me understand the concern.
>
>
>
> Bill Brooks.
>
>
>
>
>
> *From:* re-wrenches-bounces at lists.re-wrenches.org [
> mailto:re-wrenches-bounces at lists.re-wrenches.org<re-wrenches-bounces at lists.re-wrenches.org>]
> *On Behalf Of *Ray Walters
> *Sent:* Monday, April 28, 2014 2:23 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] (no subject)
>
>
>
> Interesting so does "require a tool" include taking a screw off the cover
> plate of the combiner box, too?
> What a game changer.  I'm going to Mexico for my next project; I'll
> actually enjoy even more being the sole AHJ on the project.
>
>  R.Ray Walters
>
> CTO, Solarray, Inc
>
> Nabcep Certified PV Installer,
>
> Licensed Master Electrician
>
> Solar Design Engineer
>
> 303 505-8760
>
> On 4/28/2014 2:52 PM, Michael Morningstar wrote:
>
> Readily accessible is now defined in the 2014 NEC. Installing OCPD’s
> underneath a module is a major faux paux, and I can’t imagine any AHJ
> thinking otherwise. Having to remove a module in order to reset a breaker,
> what a drag.
>
>
>
> "Capable of being reached quickly for operation, renewal or inspection
> without requiring those concerned to use a tool, to climb over, remove
> obstacle or other.”
>
>
>
> Michael
>
>
>
>
>
>
>
>
>
>   On Apr 28, 2014, at 10:29 AM, William Miller <william at millersolar.com>
> wrote:
>
>
>
>  You call it a solar panel, I call it a glass j-box cover plate.
>
> William
>
> Miller Solar
>
>
>  On Apr 28, 2014, at 9:21 AM, Jason Szumlanski <jason at fafcosolar.com>
> wrote:
>
> If that is the interpretation,
> I don't see how the breakers are "readily accessible" in a SolaDeck
> mounted anywhere, regardless of whether it is under a module. It
> requires removal of four screws (using a tool) to access the breakers
> inside the enclosure. It's all up to the AHJ. It has not been an issue
> locally here. I can see how other jurisdictions may not
> concur.
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140429/c2cc7b41/attachment-0003.html>


More information about the RE-wrenches mailing list