[RE-wrenches] Article 690, or The Haves Vs. Have Nots

Dave Click daveclick at fsec.ucf.edu
Tue Apr 29 08:44:06 PDT 2014


I think 240.24(A)(4) allows the installation of the inverter OCPDs in 
the SolaDeck hidden under a module.

** *240.24 Location in or on Premises.*
** National Electrical Code 2008 Edition *(A) Accessibility.* 
Overcurrent devices shall be readily accessible and shall be installed 
so that the center of the grip of the operating handle of the switch or 
circuit breaker, National Electrical Code 2008 Edition when in its 
highest position, is not more than 2.0 m (6 ft 7 in.) above the floor or 
working platform, unless one of the following applies:
...
(4) For overcurrent devices adjacent to utilization equipment that they 
supply, access shall be permitted to be by portable means.


And if panelboards / fused safety switches are allowed to have 
screwed-down covers over the OCPDs, I'd think that installing a 
removable module over these OCPDs would meet NEC. I guess an AHJ could 
argue that this requires TWO covers be removed, unlike a panelboard or a 
switch.

DKC


On 2014/4/29, 11:15, Jason Szumlanski wrote:
> 690.9(D) is not applicable to the original discussion because we were 
> talking about an Inverter output circuit, not a PV Source or Output 
> circuit.
>
> 690.34 may apply if you call a SolaDeck with breakers a junction box, 
> but I can see that being a stretch in the mind of many.
>
> My and Ray's question about the screws on the SolaDeck cover itself 
> requiring a tool to render it accessible is still an issue if the 
> breakers themselves need to be "readily accessible," but that would 
> also apply to a Midnite MNPV, which also has a cover with a screw.
>
>
> Jason Szumlanski
>
>
>     On 4/28/2014 5:57 PM, Bill Brooks wrote:
>>
>>     Read 690.9(D) and 690.34. Not sure where this "hysteria---run for
>>     the border" sentiment is coming from.
>>
>>     *690.9(D) Photovoltaic Source and Output Circuits. *Listed PV
>>
>>     overcurrent devices shall be required to provide overcurrent
>>
>>     protection in PV source and output circuits. The overcurrent
>>
>>     devices shall be accessible but shall not be required to
>>
>>     be readily accessible.
>>
>>     *690.34 Access to Boxes. *Junction, pull, and outlet boxes
>>
>>     located behind modules or panels shall be so installed that
>>
>>     the wiring contained in them can be rendered accessible
>>
>>     directly or by displacement of a module(s) or panel(s) secured
>>
>>     by removable fasteners and connected by a flexible
>>
>>     wiring system.
>>
>>     This is not a change. Please help me understand the concern.
>>
>>     Bill Brooks.
>>
>>     *From:*re-wrenches-bounces at lists.re-wrenches.org
>>     <mailto:re-wrenches-bounces at lists.re-wrenches.org>
>>     [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of
>>     *Ray Walters
>>     *Sent:* Monday, April 28, 2014 2:23 PM
>>     *To:* RE-wrenches
>>     *Subject:* Re: [RE-wrenches] (no subject)
>>
>>     Interesting so does "require a tool" include taking a screw off
>>     the cover plate of the combiner box, too?
>>     What a game changer.  I'm going to Mexico for my next project;
>>     I'll actually enjoy even more being the sole AHJ on the project.
>>
>>     R.Ray Walters
>>     CTO, Solarray, Inc
>>     Nabcep Certified PV Installer,
>>     Licensed Master Electrician
>>     Solar Design Engineer
>>     303 505-8760  <tel:303%20505-8760>
>>
>>     On 4/28/2014 2:52 PM, Michael Morningstar wrote:
>>
>>         Readily accessible is now defined in the 2014 NEC. Installing
>>         OCPD's underneath a module is a major faux paux, and I can't
>>         imagine any AHJ thinking otherwise. Having to remove a module
>>         in order to reset a breaker, what a drag.
>>
>>         "Capable of being reached quickly for operation, renewal or
>>         inspection without requiring those concerned to use a tool,
>>         to climb over, remove obstacle or other."
>>
>>         Michael
>>
>>
>>
>>         On Apr 28, 2014, at 10:29 AM, William Miller
>>         <william at millersolar.com <mailto:william at millersolar.com>> wrote:
>>
>>
>>
>>             You call it a solar panel, I call it a glass j-box cover
>>             plate.
>>
>>             William
>>
>>             Miller Solar
>>
>>
>>                 On Apr 28, 2014, at 9:21 AM, Jason Szumlanski
>>                 <jason at fafcosolar.com <mailto:jason at fafcosolar.com>>
>>                 wrote:
>>
>>                 If that is the interpretation,
>>                 I don't see how the breakers are "readily accessible"
>>                 in a SolaDeck
>>                 mounted anywhere, regardless of whether it is under a
>>                 module. It
>>                 requires removal of four screws (using a tool) to
>>                 access the breakers
>>                 inside the enclosure. It's all up to the AHJ. It has
>>                 not been an issue
>>                 locally here. I can see how other jurisdictions may not
>>                 concur.
>>
>
>
>     _______________________________________________
>     List sponsored by Home Power magazine
>
>     List Address: RE-wrenches at lists.re-wrenches.org
>     <mailto:RE-wrenches at lists.re-wrenches.org>
>
>     Change email address & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>     <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches..org>
>
>     List-Archive:
>     http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>     List rules & etiquette:
>     www.re-wrenches.org/etiquette.htm
>     <http://www.re-wrenches.org/etiquette.htm>
>
>     Check out participant bios:
>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140429/b3d3ec77/attachment-0003.html>


More information about the RE-wrenches mailing list