Mac:

 

Is your system 120 or 120/240?  If it is 120 only and if your shared
neutrals are part of a multi-wire branch circuit, you have problems.  The
only solution I know of is to combine the circuits so they are on the same
phase and share the same OCPD.  Otherwise it’s time to rewire.

 

If these are not multi-wire branch circuits, I am not sure why they are
sharing a neutral.  In any case, the circuits should be combined or rewired.

 

William Miller

 

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Mac Lewis
Sent: Tuesday, April 08, 2014 9:22 PM
To: RE-wrenches
Subject: [RE-wrenches] shared neutral critical load panel

 

Hello wrenches,

 

When installing hybrid systems and consolidating critical load panel
circuits, how do you deal with shared neutrals?  We have moved both of these
loads into the critical load panel or negotiated both loads being left out
of the critical load panel because of this shared neutral issue.  Is there
any code-compliant way of splitting these up?

 

We have ran into some unfortunate neutral sharing load pairings lately that
have been a headache and should never have shared a neutral.

 

Thanks in advance
-- 

 

 

 

Mac Lewis