[RE-wrenches] GEC sizing for a high amp, low voltage PV system with microinverters
Aladdin Solar
cpickard at aladdinsolar.com
Wed Sep 18 22:52:24 PDT 2013
Thanks Brian. That helps.
Charlie Pickard
NABCEP Certified PV Installation Professional ™
Aladdin Solar,LLC
----- Original Message -----
From: Brian Mehalic
To: Aladdin Solar ; RE-wrenches
Sent: Wednesday, September 18, 2013 4:17 PM
Subject: Re: [RE-wrenches] GEC sizing for a high amp, low voltage PV system with microinverters
Sole connection indicates that a GEC is connected to only one type of grounding electrode. This term is easily mis- understood. For example, a GEC can be connected to more than one grounding electrode—say, two ground rods—and still be considered to have a sole connection. Similarly, multiple GECs connected to the same grounding electrode are each considered to have a sole connection. When GECs have a sole connection, their maximum size is limited per NEC Sections 250.66 for an ac system and 250.166 for a dc system. The 2014 NEC adds some clarification on this.
Brian Mehalic
NABCEP Certified Solar PV Installation Professional™ R031508-59
IREC ISPQ Certified Affiliated Instructor/PV US-0132
PV Curriculum Developer and Instructor
Solar Energy International
http://www.solarenergy.org
On Wed, Sep 18, 2013 at 4:52 PM, Aladdin Solar <cpickard at aladdinsolar.com> wrote:
Yes, Jay, this is a TenKSolar system -- they certainly do have a habit of taking the 'thinking outside the box' approach!
The microinverter manufacturer states in their installation manual, "Connect the grounding electrode conductor to the microinverter ground clamp" so it's quite clear we are dealing with GEC rules.
Thanks for all your comments and the reminder of the NEC 250.166(C) exception which I hadn't really connected with before.
I'm having difficulty understanding what the requirement in that paragraph actually means. When it states "that portion of the grounding electrode conductor that is the sole connection to the grounding electrode shall not be required to be larger than 6AWG..." -- what does "that portion" and "sole connection" mean? If we have a number of GEC branches from that are irreversably spliced to a single 6AWG conductor bonded to the grounding electrode, do those various GECs affect the "that portion" and "sole connection" at all?
Charlie Pickard
NABCEP Certified PV Installation Professional ™
Aladdin Solar, LLC
----- Original Message -----
From: Bill Brooks
To: 'RE-wrenches'
Sent: Wednesday, September 18, 2013 2:42 PM
Subject: Re: [RE-wrenches] GEC sizing for a high amp,low voltage PV system with microinverters
Nick,
Thanks for the clarification—it is a mysterious threaded hole….
Bill.
From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Nick Soleil
Sent: Wednesday, September 18, 2013 10:19 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] GEC sizing for a high amp, low voltage PV system with microinverters
Hi Bill and wrenches,
To clarify, our new Enphase M250 microinverter does not have a grounding terminal. The grounding of the M250 will be provided through the Engage cable. We only have a hole in the lid, in the rare case that a lug will be desired or required by the AHJ, but we do not provide the grounding clip with the microinverter. A grounding terminal can be added to the microinverter. We have an application note on alternate grounding methods for the M250, if needed.
__________ Information from ESET NOD32 Antivirus, version of virus signature database 8815 (20130918) __________
The message was checked by ESET NOD32 Antivirus.
http://www.eset.com
--------------------------------------------------------------------------
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
__________ Information from ESET NOD32 Antivirus, version of virus signature database 8815 (20130918) __________
The message was checked by ESET NOD32 Antivirus.
http://www.eset.com
__________ Information from ESET NOD32 Antivirus, version of virus signature database 8817 (20130918) __________
The message was checked by ESET NOD32 Antivirus.
http://www.eset.com
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
__________ Information from ESET NOD32 Antivirus, version of virus signature database 8817 (20130918) __________
The message was checked by ESET NOD32 Antivirus.
http://www.eset.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130919/6aa9fdcc/attachment-0004.html>
More information about the RE-wrenches
mailing list