[RE-wrenches] SW AGS

Eric.Bentsen at schneider-electric.com Eric.Bentsen at schneider-electric.com
Wed Aug 7 14:14:08 PDT 2013


It's an XW system.....SW doesn't have event codes. 
Starting the gen manually just means it will keep running until he stops 
it.
We need to see how much current is flowing, and what's going on with 
battery voltage.
If you are going to the site, give me a call when you get there.
866-519-1470
Rgds,
_____________________________________________________________________________________ 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bentsen at schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
"SunHarvest" <eric at harvesthesun.com>
To:
"RE-wrenches" <re-wrenches at lists.re-wrenches.org>
Date:
08/07/2013 02:08 PM
Subject:
Re: [RE-wrenches] SW AGS
Sent by:
re-wrenches-bounces at lists.re-wrenches.org



Sounds like you talked to the right guy, that's his info...except that he 
has, according to what he told me, an SW not an XW. I'm assuming he's 
maybe at 50% capacity on his original 1260Ah bank based on everything he 
told me this morning. He did say that his bank will last him through the 
night and that he has some pretty hefty air conditioning loads. He also 
said he had equalized in the past but not in the last 18 months. I'm just 
not convinced that his batteries are shot. But all this battery talk may 
be beside the point if he's not experiencing the same on/off cycling 
problem when he manually starts the genny, right? That is, assuming the 
disco settings remain in effect regardless of start mechanism. Thanks for 
indulging me tocayo.
 
Eric
SunHarvest
001.530.798.3738 (Cell)
----- Original Message ----- 
From: Eric.Bentsen at schneider-electric.com 
To: RE-wrenches 
Sent: Wednesday, August 07, 2013 12:54 PM
Subject: Re: [RE-wrenches] SW AGS


Hi Eric, 
 Sounded like bad batteries to me also (I think he called in this AM). He 
has (2) XW6048 units that are 
capable of 200ADC between them, and he also has 1260Ah of flooded 
capacity. DC Start V is set for 46.5V, so if we assume he was close to 50% 

discharge (depending on load), it should take almost 2 hours to reach the 
bulk voltage (80% replaced). His batteries were ramping up to bulk 
in just a couple of minutes, meaning the batteries were not absorbing the 
charge. I have heard varying opinions on the symptoms of sulfation, 
but it does sound like a battery issue (5 yrs old). He was advised to 
equalize to try and recover them (he has never done this), or replace 
them. 
Rgds, 

_____________________________________________________________________________________ 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bentsen at schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 



From: 
"SunHarvest" <eric at harvesthesun.com> 
To: 
"RE-wrenches" <re-wrenches at lists.re-wrenches.org> 
Date: 
08/07/2013 12:39 PM 
Subject: 
[RE-wrenches] SW AGS 
Sent by: 
re-wrenches-bounces at lists.re-wrenches.org




I read through the archives on the XW AGS thread but have a query on 
behalf of a customer with an SW AGS issue. I'm heading out to the remote 
site tomorrow and would like, if possible, to show up knowing what I might 
be up against. 
  
The customer recently replaced his AGS for his two SW 6048s and then 
upgraded his firmware a week later. He reported that his problem with the 
AGS began after firmware upgrade. Here's the particular issue: 
  
AGS will try to start the 15.8kW Multi-Quip genny due to low battery 
voltage (event 306 DCV start). After about 5 minutes the AGS will stop the 
genny due to battery absorption level reached (event 313 ABS stop). The 
AGS will go through this event 306/313 cycle on and off until the 
homeowner shuts down the AGS. To me this sounds like bad batteries. But, 
the homeowner says this cycling does not occur when he manually starts the 
generator. This doesn't sound like a complicated problem but so far I'm 
unfamiliar with the SW AGS. So, I would greatly appreciate any insight you 
guys can offer me. 
  
Thanks!! 
  
Eric
SunHarvest
001.530.798.3738 (Cell) 

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130807/93fabab1/attachment-0004.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 11065 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130807/93fabab1/attachment-0008.jpe>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 11065 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130807/93fabab1/attachment-0009.jpe>


More information about the RE-wrenches mailing list