[RE-wrenches] Enphase failures
Carl Adams
swingjunkie at gmail.com
Mon Aug 5 03:02:01 PDT 2013
William Dorsett,
I've attached the spreadsheet with the full stats
Marco,
Enphase is paying $150 for the service call replacement. Add $25 for each
additional inverter replaced in the same trip. For the full site
replacement we quoted Enphase a price for the labor and they accepted it as
reasonable.
To echo William Miller's comment it would be good to see stats for
competitive products.
I hope this is helpful
With Regards
Carl Adams
SunRock Solar
On Mon, Aug 5, 2013 at 1:43 AM, Marco Mangelsdorf <marco at pvthawaii.com>wrote:
> Very helpful, Carl. Thanks.****
>
> ** **
>
> Might I ask what kind of compensation you’re getting from Enphase for your
> time and repeated trips to the site?****
>
> ** **
>
> marco****
>
> ** **
>
> *From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
> re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *Carl Adams
> *Sent:* Sunday, August 04, 2013 4:26 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Enphase failures****
>
> ** **
>
> Marco,****
>
> ** **
>
> Here is a summary of our experience with Enphase to date****
>
> 13.1%****
>
> overall failure rate****
>
> 25.6% ****
>
> M190 failure rate****
>
> 25.0% ****
>
> D380 failure rate****
>
> 2.1% ****
>
> M210 failure rate****
>
> 5.6% ****
>
> M215 failure rate****
>
> ** **
>
> We have had two full site upgrades last year. One from M190s - 215s, the
> other from D380s to M215s. No problems at those sites since the swap out.
> ****
>
> We have two other M190 sites in line to be swapped for 215s once the 90
> day monitoring period is up. ****
>
> ** **
>
> Just swapped 3 of 15 inverters on a site last week. When I showed up with
> the 3 new inverters two more had died, they are now enroute from Enphase.
> ****
>
> Those failures are reflected in the above statistics.****
>
> ** **
>
> With Regards****
>
> Carl Adams****
>
> SunRock Solar****
>
> ** **
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130805/f19988f8/attachment-0004.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Enphase Failures Summary.pdf
Type: application/pdf
Size: 42670 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130805/f19988f8/attachment-0007.pdf>
More information about the RE-wrenches
mailing list