[RE-wrenches] Tape on modules for wire management
Dave Click
daveclick at fsec.ucf.edu
Wed Jul 10 19:21:26 PDT 2013
All these manufacturers making cable clips are going to be so upset when
they learn that we know about this quick, cost-effective wire management
method!
You could start with 110.3(B) where the module installation manual may
prohibit anything adhered to the back of the module.
Or 338.10(B)(4)(b) -> 334.30, relating to properly supporting the cables.
Or [2011] 690.4(E) "qualified personnel" or 110.12 "neat and workmanlike
manner," which is probably the most straightforward way to call someone
an idiot if you want to use the NEC exclusively.
DKC
On 2013/7/10 21:37, jay peltz wrote:
> Hi all,
>
> You code wonks can help out here
>
> I had a friend ask about an install he saw that used electrical tape to attach the PV wires to the modules, yep actually taping them to the back of the module.
>
> I'm having trouble figuring out if this actually breaks any codes and if so which ones
>
> Then there is the whole ul,listing of the modules and is that approved?
>
> Thanks,
>
> Jay
> Peltz power
>
>