I don't believe this would work; official metal-clad cable would, but 
not armored cable. Metal-clad only works under the 2011 NEC, and only 
then when it meets 250.118(10).


On 2013/4/11 19:24, Hilton Dier III wrote:
> I asked this one last year and got a few "That's interesting" responses,
> but nobody actually came up with an answer. Perhaps it was too obvious.
>
> I have been looking at Teck 90 waterproof metallic armored cable as a
> possibility for DC wire runs. This is the stuff:
> http://www.onestopbuy.com/omni-wire-cable/T30804-40643.asp It seems to
> be roughly the cost of wire and conduit and a lot easier to run. It
> looks versatile:
>
> "Suitable for use in ventilated, non-ventilated and ladder cable trays,
> direct earth burial or raceways, and for exposed or concealed wiring in
> wet, damp or dry locations. Suitable for use in wet or dry locations
> when installed in accordance with the NEC."
>
> The question is, would this stuff be acceptable code-wise for
> metallic-contained interior DC wire runs per 690.31 (E)? You'd think so,
> but I'd want to be sure before buying a reel of this stuff.
>
> Thanks, wrenches!
>
> Hilton
>
> --
> Hilton Dier III
> Renewable Energy Design
> Partner, Solar Gain LLC
> 453 East Hill Rd.
> Middlesex, VT 05602
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>



More information about the RE-wrenches mailing list