[RE-wrenches] Fuse sizing in battery circuits

Drake drake.chamberlin at redwoodalliance.org
Tue Apr 9 08:03:54 PDT 2013


Thanks William,

I just bought some fuses.

At 10:00 AM 4/9/2013, you wrote:
>Content-Type: multipart/related;
>         boundary="----=_NextPart_000_0046_01CE3500.A0F44C00"
>Content-Language: en-us
>
>This topic comes up often enough that we ought 
>to mention a yellowed article in Home Power, 
>(1992 Issue 27, pg 26). Christopher Freitas 
>wrote Overcurrent Protection for Battery-Powered 
>Systems where he describes experiments he did 
>back when he was with Ananda. He put a 2000 A 
>Big Switch to initiate a short (4/0 cable) 
>between the terminals on a set of four golf cart 
>batteries (2 strings @ 12V). In series, he put 
>in a 500A Shunt so he could measure current 
>passing and various fuses and breakers. “For 
>comparison, we decided to directly short the 
>battery
the meter read 6960 amps peak current 
>(three seconds) 
during each test the 4/0 cable 
>lifted off the ground 4 inches into the air by 
>the forces generated by the extremely high 
>current..” They videoed the 250 A ANN buss fuses 
>arc and smoke; the 200A Heinemann Series AM 
>breakers (paralleled ones that maybe Roy 
>mentioned) went 3 seconds without breaking and 
>the video showed a flash and blue smoke.
>175A ITE breaker with 42,000 AIC “simply 
>tripped
but still allowed a peak current of 2960 amps
>200A Class T Littlefuse “opened promptly with no 
>external signs of stress
1920 amps peak current”
>Christopher’s recommendations:
>“Every AE system must have overcurrent 
>protection able to interrupt the maximum current 
>available from the batteries. For most systems, 
>the main protection should use current limiting 
>high AIC fuses, such as a Class T or Class R. A 
>disconnect switch which allows the fuse to be 
>safely changed should be included. A lower cost 
>alternative is to mount the fuse in a fuse 
>holder without a disconnect. Although the fuse 
>would always be electrically hot,  it normally 
>would not be changed during the life of the 
>system. The fuse holder should be mounted 
>outside the battery enclosure. Fuses should not 
>be bolted directly onto the battery terminal, as 
>they are not designed to handle the physical 
>stresses that can occur without the protection of a fuse holder.
>
>Fuses which have exposed elements, such as ANN 
>fuses, should not be used because they are not 
>current limiting and have only 2500 amps AIC. 
>They also may be a significant hazard when installed near batteries.
>
>High AIC breakers, like the Heinemann Series CF 
>(25,000 Amps AIC @ 65VDC) can provide 
>overcurrent protection for individual items. 
>They cannot be used to protect lower AIC 
>breakers. This eliminates their use as a main disconnect in most systems.
>
>Low AIC breakers, like the Heinemann Series AM 
>(5000A AIC @65 VDC) or the Square-D QO (5000A @ 
>125 VDC) can be used in load distribution 
>centers and components, but must be protected by 
>a current limiting fuse. Using low-AIC breakers 
>alone will not provide sufficient protection 
>with a battery system and may be a significant 
>hazard during short circuit situations.”
>
>It won’t pull up anymore on HP’s article search 
>but probably Michael has a copy he could post for those interested.
>
>Bill  Dorsett
>Manhattan, KS
>From: re-wrenches-bounces at lists.re-wrenches.org 
>[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of John Berdner
>Sent: Monday, April 08, 2013 7:25 PM
>To: Allan at positiveenergysolar.com; RE-wrenches
>Subject: Re: [RE-wrenches] Fuse sizing in battery circuits
>
>Allan:
>
>A pretty accurate retention of the Grass Valley / Nevada County through 2000.
>You only missed the Trace to Xantrex 
>“acquisition” that was the start of the divorce J
>
>Class T fuses provide better protection for 
>battery based inverters – always been that way.
>The move to breakers was a cost reduction issues 
>when Trace introduced the DC-250.
>I still contend that the way the DC-250 did it 
>was a Code violation when used with PV in the 
>box (current from all sources issue) but that is history.
>
>For high current applications the Boltswitch 
>Pull outs (the ones we used in the Power 
>Centers) came in 100A, 200A and 400 A sizes and 1, 2, and 3 pole versions.
>I think they are still made today.
>Still the best way to do currents above 250 Amps.
>You can do a Eaton / GJ1P breaker up to 750 Amps but they are Spin Dee.
>
>As you noted you can use a single pull out to do up to 3 battery strings.
>You make a copper “comb” to parallel separate 
>fused inputs to a single inverter.
>If you have more than one inverter you can have 
>“back to back” fuse blocks with an H-H-H shaped bus bar set up.
>The biggest one I recall we did was a 12 400 A 
>battery/PV  inputs going to 8 SW inverters.
>You size the copper bus bars for 1000 A / square 
>inch of cross section and you are good to go 
>(this is from the UL 508 design guide).
>
>Best Regards,
>
>John Berdner
>General Manager, North America
>
>SolarEdge Technologies, Inc.
>3347 Gateway Boulevard, Fremont CA 94538 
>USA  (*Please note of our new address.)
>T: 510.498.3200, X 747
>M: 530.277.4894
>
>From: 
><mailto:re-wrenches-bounces at lists.re-wrenches.org>re-wrenches-bounces at lists.re-wrenches.org 
>[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Allan Sindelar
>Sent: Friday, April 05, 2013 9:00 PM
>To: RE-wrenches
>Subject: Re: [RE-wrenches] Fuse sizing in battery circuits
>
>William,
>For this I went deep into the catacombs of our 
>hardware file cabinet, and quickly found a 1996 
>spec sheet from an Ananda Power Technologies 
>SafeT-Block. For the young'uns, Ananda was a 
>quality company, the originator of the listed 
>Powercenter - the breaker and terminal block 
>hardware that is part of every batttery-based 
>system nowadays. Ananda became APT, then Pulse, 
>then part of Trace (the PC250 and PC500) as part 
>of a short-lived marriage followed by a messy 
>divorce, the results of which led, as an act of 
>revenge insurrection, to the introduction into 
>the U.S. market of the Sunny Boy and AC-coupled 
>systems, and the rest is even more wacky 
>history. But I digress, after a run-on sentence 
>bad enough that my high school English teacher is rolling over in her grave...
>
>I have attached a scan of page two of the spec 
>sheet. In the upper left corner is a chart of 
>current vs. time for a Class T fuse. Once I 
>understood this chart I never again worried 
>about nuisance tripping, as whether described as 
>fast-acting or not, Class T fuses have an 
>inherent surge capacity of about 2 1/2 times 
>their rating, and thus can handle surges.
>
>If you put them on individual battery strings, 
>the point is to prevent overcurrent on one 
>string, which is only likely to occur when 
>either 1) a terminal is corroded sufficiently 
>that one string fails to carry its share of the 
>load or charge (we have seen this) or 2) one 
>string fails when the batteries reach 
>end-of-life. When the Class T fuses blows in 
>that situation it has done its job.
>Allan
>Allan Sindelar
><mailto:Allan at positiveenergysolar.com>Allan at positiveenergysolar.com
>NABCEP Certified Photovoltaic Installer
>NABCEP Certified Technical Sales Professional
>New Mexico EE98J Journeyman Electrician
>Founder and Chief Technology Officer
>Positive Energy, Inc.
>3209 Richards Lane (note new address)
>Santa Fe, New Mexico 87507
>505 424-1112
><http://www.positiveenergysolar.com/>www.positiveenergysolar.com
>
>[]
>
>
>On 4/5/2013 8:29 PM, William Miller wrote:
>Friends:
>
>Good topic.  Some questions:
>
>1. Most manufacturer's present an installation 
>guide that shows one OCPD in the battery circuit 
>and that is in the BOS cabinet.  This means the 
>battery leads are unprotected.  Do we need an OPCD at the battery terminals?
>
>2. Class T fuses are generally recommended for 
>this application.  The data shows them as "fast 
>acting."  Is this a problem?  Will they act too 
>fast and open during normal surge loads?
>
>Thanks in advance!
>
>William Miller
>
>
>
>
>
>Troy,
>
>Overcurrent device size is matched to the 
>conductor size. The inverse time constant nature 
>of an overcurrent device can typically handle 
>the surge currents as long as conductor sizing 
>has truly been done correctly for the conductor. 
>Circuit breakers are preferred to fuses because they can be reset.
>
>There has been volumes written on this issue. 
>The constant current at lowest battery voltage 
>should be used, plus the ac ripple content on 
>the battery circuit. This is usually a much 
>larger conductor than your average designer will 
>plan for. The best thing is to look at Midnight, 
>Outback, and Schneider and see what size 
>overcurrent devices they require for their 
>products. That will give you a good clue as to 
>how to size the conductor and overcurrent device.
>
>Bill.
>
>From: 
><mailto:re-wrenches-bounces at lists.re-wrenches.org>re-wrenches-bounces at lists.re-wrenches.org 
>[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Troy Harvey
>Sent: Friday, April 05, 2013 3:38 PM
>To: RE-wrenches
>Subject: [RE-wrenches] Fuse sizing in battery circuits
>
>I've got a question about battery string fusing. 
>Typically we size the wire from the batteries to 
>the inverter based on continuous rating 
>procedures (max power/efficiency)*125%.
>
>However a 6kW inverter, can peak at 12kW for 
>5-10 seconds, doubling the source current. That 
>is no big deal for the wire, because it is a 
>short time frame... little heat will be 
>generated. However, in fusing the sub-strings, 
>you need to account for that peak surge current 
>so you don't blow fuses all the time. But if you 
>put a 500-1000 amp fuse on a 4/0 wire, above the 
>max surge draw of the inverter, the wire will be 
>under-protected for its ampacity rating. Any thoughts on the catch-22?
>
>
>
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: 
><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>
>Change email address & settings:
><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
><http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>
>
>CONFIDENTIALITY NOTICE: This e-mail and its 
>attachments are intended only for the use of the 
>individual or entity who is the intended 
>recipient and may contain information that is 
>privileged, confidential and exempt from 
>disclosure or any type of use under applicable 
>law. If the reader of this e-mail is not the 
>intended recipient, or the employee, agent, or 
>representative responsible for delivering the 
>e-mail to the intended recipient, you are hereby 
>notified that any dissemination, distribution, 
>copying, or other use of this e-mail is strictly 
>prohibited. If you have received this e-mail in 
>error, please reply immediately to the sender.
>P  Please think of the environment before printing this email
>
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130409/b91d25b4/attachment-0004.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 7a74a5.png
Type: image/png
Size: 33435 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130409/b91d25b4/attachment-0007.png>


More information about the RE-wrenches mailing list