[RE-wrenches] Fuse sizing in battery circuits

Kent Osterberg kent at coveoregon.com
Tue Apr 9 08:35:55 PDT 2013


Bill,

I have all of those old HP issues in my library and once in a while they 
are handy. Thanks for prompting me to take a look at this one again. It 
should be an eye-opener for folks that the 5000 AIC rated breakers were 
pretty much a failure at opening a shorted set of four golf-cart 
batteries at 12 volts. This article makes me wonder how the small DIN 
rail mounted CBI breakers and small panel mount breakers used by Midnite 
and Outback would do. I fear not very well, and yet they are connected 
directly to the battery in thousands of systems.

Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com


On 4/9/2013 7:00 AM, William Dorsett wrote:
>
> This topic comes up often enough that we ought to mention a yellowed 
> article in Home Power, (1992 Issue 27, pg 26). Christopher Freitas 
> wrote /Overcurrent Protection for Battery-Powered Systems /where he 
> describes experiments he did back when he was with Ananda. He put a 
> 2000 A Big Switch to initiate a short (4/0 cable) between the 
> terminals on a set of four golf cart batteries (2 strings @ 12V). In 
> series, he put in a 500A Shunt so he could measure current passing and 
> various fuses and breakers. "For comparison, we decided to directly 
> short the battery...the meter read 6960 amps peak current (three 
> seconds) ...during each test the 4/0 cable lifted off the ground 4 
> inches into the air by the forces generated by the extremely high 
> current.." They videoed the 250 A ANN buss fuses arc and smoke; the 
> 200A Heinemann Series AM breakers (paralleled ones that maybe Roy 
> mentioned) went 3 seconds without breaking and the video showed a 
> flash and blue smoke.
>
> 175A ITE breaker with 42,000 AIC "simply tripped...but still allowed a 
> peak current of 2960 amps
>
> 200A Class T Littlefuse "opened promptly with no external signs of 
> stress...1920 amps peak current"
>
> Christopher's recommendations:
>
> "Every AE system must have overcurrent protection able to interrupt 
> the maximum current available from the batteries. For most systems, 
> the main protection should use current limiting high AIC fuses, such 
> as a Class T or Class R. A disconnect switch which allows the fuse to 
> be safely changed should be included. A lower cost alternative is to 
> mount the fuse in a fuse holder without a disconnect. Although the 
> fuse would always be electrically hot,  it normally would not be 
> changed during the life of the system. The fuse holder should be 
> mounted outside the battery enclosure. Fuses should not be bolted 
> directly onto the battery terminal, as they are not designed to handle 
> the physical stresses that can occur without the protection of a fuse 
> holder.
>
> Fuses which have exposed elements, such as ANN fuses, should not be 
> used because they are not current limiting and have only 2500 amps 
> AIC. They also may be a significant hazard when installed near batteries.
>
> High AIC breakers, like the Heinemann Series CF (25,000 Amps AIC @ 
> 65VDC) can provide overcurrent protection for individual items. They 
> cannot be used to protect lower AIC breakers. This eliminates their 
> use as a main disconnect in most systems.
>
> Low AIC breakers, like the Heinemann Series AM (5000A AIC @65 VDC) or 
> the Square-D QO (5000A @ 125 VDC) can be used in load distribution 
> centers and components, but must be protected by a current limiting 
> fuse. Using low-AIC breakers alone will not provide sufficient 
> protection with a battery system and may be a significant hazard 
> during short circuit situations."
>
> It won't pull up anymore on HP's article search but probably Michael 
> has a copy he could post for those interested.//
>
> Bill Dorsett
>
> Manhattan, KS
>
> *From:*re-wrenches-bounces at lists.re-wrenches.org 
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *John 
> Berdner
> *Sent:* Monday, April 08, 2013 7:25 PM
> *To:* Allan at positiveenergysolar.com; RE-wrenches
> *Subject:* Re: [RE-wrenches] Fuse sizing in battery circuits
>
> Allan:
>
> A pretty accurate retention of the Grass Valley / Nevada County 
> through 2000.
>
> You only missed the Trace to Xantrex "acquisition" that was the start 
> of the divorce J
>
> Class T fuses provide better protection for battery based inverters -- 
> always been that way.
>
> The move to breakers was a cost reduction issues when Trace introduced 
> the DC-250.
>
> I still contend that the way the DC-250 did it was a Code violation 
> when used with PV in the box (current from all sources issue) but that 
> is history.
>
> For high current applications the Boltswitch Pull outs (the ones we 
> used in the Power Centers) came in 100A, 200A and 400 A sizes and 1, 
> 2, and 3 pole versions.
>
> I think they are still made today.
>
> Still the best way to do currents above 250 Amps.
>
> You can do a Eaton / GJ1P breaker up to 750 Amps but they are Spin Dee.
>
> As you noted you can use a single pull out to do up to 3 battery strings.
>
> You make a copper "comb" to parallel separate fused inputs to a single 
> inverter.
>
> If you have more than one inverter you can have "back to back" fuse 
> blocks with an H-H-H shaped bus bar set up.
>
> The biggest one I recall we did was a 12 400 A battery/PV  inputs 
> going to 8 SW inverters.
>
> You size the copper bus bars for 1000 A / square inch of cross section 
> and you are good to go (this is from the UL 508 design guide).
>
> Best Regards,
>
> John Berdner
>
> General Manager, North America
>
> SolarEdge Technologies, Inc.
>
> 3347 Gateway Boulevard, Fremont CA 94538 USA */(*Please note of our 
> new address.)/*
> T: 510.498.3200, X 747
>
> M: 530.277.4894
>
> *From:*re-wrenches-bounces at lists.re-wrenches.org 
> <mailto:re-wrenches-bounces at lists.re-wrenches.org> 
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of 
> *Allan Sindelar
> *Sent:* Friday, April 05, 2013 9:00 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Fuse sizing in battery circuits
>
> William,
> For this I went deep into the catacombs of our hardware file cabinet, 
> and quickly found a 1996 spec sheet from an Ananda Power Technologies 
> SafeT-Block. For the young'uns, Ananda was a quality company, the 
> originator of the listed Powercenter - the breaker and terminal block 
> hardware that is part of every batttery-based system nowadays. Ananda 
> became APT, then Pulse, then part of Trace (the PC250 and PC500) as 
> part of a short-lived marriage followed by a messy divorce, the 
> results of which led, as an act of revenge insurrection, to the 
> introduction into the U.S. market of the Sunny Boy and AC-coupled 
> systems, and the rest is even more wacky history. But I digress, after 
> a run-on sentence bad enough that my high school English teacher is 
> rolling over in her grave...
>
> I have attached a scan of page two of the spec sheet. In the upper 
> left corner is a chart of current vs. time for a Class T fuse. Once I 
> understood this chart I never again worried about nuisance tripping, 
> as whether described as fast-acting or not, Class T fuses have an 
> inherent surge capacity of about 2 1/2 times their rating, and thus 
> can handle surges.
>
> If you put them on individual battery strings, the point is to prevent 
> overcurrent on one string, which is only likely to occur when either 
> 1) a terminal is corroded sufficiently that one string fails to carry 
> its share of the load or charge (we have seen this) or 2) one string 
> fails when the batteries reach end-of-life. When the Class T fuses 
> blows in that situation it has done its job.
> Allan
>
> *Allan Sindelar*
> Allan at positiveenergysolar.com <mailto:Allan at positiveenergysolar.com>
> NABCEP Certified Photovoltaic Installer
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Founder and Chief Technology Officer
> *Positive Energy, Inc.*
> 3209 Richards Lane (note new address)
> Santa Fe, New Mexico 87507
> *505 424-1112*
> www.positiveenergysolar.com <http://www.positiveenergysolar.com/>
>
>
> On 4/5/2013 8:29 PM, William Miller wrote:
>
>     Friends:
>
>     Good topic.  Some questions:
>
>     1. Most manufacturer's present an installation guide that shows
>     one OCPD in the battery circuit and that is in the BOS cabinet. 
>     This means the battery leads are unprotected.  Do we need an OPCD
>     at the battery terminals?
>
>     2. Class T fuses are generally recommended for this application. 
>     The data shows them as "fast acting."  Is this a problem?  Will
>     they act too fast and open during normal surge loads?
>
>     Thanks in advance!
>
>     William Miller
>
>
>
>
>
>     Troy,
>
>     Overcurrent device size is matched to the conductor size. The
>     inverse time constant nature of an overcurrent device can
>     typically handle the surge currents as long as conductor sizing
>     has truly been done correctly for the conductor. Circuit breakers
>     are preferred to fuses because they can be reset.
>
>     There has been volumes written on this issue. The constant current
>     at lowest battery voltage should be used, plus the ac ripple
>     content on the battery circuit. This is usually a much larger
>     conductor than your average designer will plan for. The best thing
>     is to look at Midnight, Outback, and Schneider and see what size
>     overcurrent devices they require for their products. That will
>     give you a good clue as to how to size the conductor and
>     overcurrent device.
>
>     Bill.
>
>     *From:* re-wrenches-bounces at lists.re-wrenches.org
>     <mailto:re-wrenches-bounces at lists.re-wrenches.org>
>     [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of
>     *Troy Harvey
>     *Sent:* Friday, April 05, 2013 3:38 PM
>     *To:* RE-wrenches
>     *Subject:* [RE-wrenches] Fuse sizing in battery circuits
>
>     I've got a question about battery string fusing. Typically we size
>     the wire from the batteries to the inverter based on continuous
>     rating procedures (max power/efficiency)*125%.
>
>     However a 6kW inverter, can peak at 12kW for 5-10 seconds,
>     doubling the source current. That is no big deal for the wire,
>     because it is a short time frame... little heat will be generated.
>     However, in fusing the sub-strings, you need to account for that
>     peak surge current so you don't blow fuses all the time. But if
>     you put a 500-1000 amp fuse on a 4/0 wire, above the max surge
>     draw of the inverter, the wire will be under-protected for its
>     ampacity rating. Any thoughts on the catch-22?
>
>
>
>     _______________________________________________
>
>     List sponsored by Home Power magazine
>
>       
>
>     List Address:RE-wrenches at lists.re-wrenches.org  <mailto:RE-wrenches at lists.re-wrenches.org>
>
>       
>
>     Change email address & settings:
>
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>       
>
>     List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>       
>
>     List rules & etiquette:
>
>     www.re-wrenches.org/etiquette.htm  <http://www.re-wrenches.org/etiquette.htm>
>
>       
>
>     Check out participant bios:
>
>     www.members.re-wrenches.org  <http://www.members.re-wrenches.org>
>
>       
>
> CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended 
> only for the use of the individual or entity who is the intended 
> recipient and may contain information that is privileged, confidential 
> and exempt from disclosure or any type of use under applicable law. If 
> the reader of this e-mail is not the intended recipient, or the 
> employee, agent, or representative responsible for delivering the 
> e-mail to the intended recipient, you are hereby notified that any 
> dissemination, distribution, copying, or other use of this e-mail is 
> strictly prohibited. If you have received this e-mail in error, please 
> reply immediately to the sender.
>
> *P*  Please think of the environment before printing this email
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130409/1c86dc60/attachment-0003.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 33435 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130409/1c86dc60/attachment-0006.png>


More information about the RE-wrenches mailing list