[RE-wrenches] Cable tray
Glenn Burt
glenn.burt at glbcc.com
Mon Mar 25 15:34:37 PDT 2013
392.3(B)1
This was also pointed out in a recent article in Solar Pro talking about
Wire Management issues.
From: Chris Mason [mailto:cometenergysystems at gmail.com]
Sent: Monday, March 25, 2013 6:17 PM
To: glenn.burt at glbcc.com; RE-wrenches
Subject: Re: [RE-wrenches] Cable tray
What part of 392 would be a problem?
On Mon, Mar 25, 2013 at 6:12 PM, Glenn Burt <glenn.burt at glbcc.com> wrote:
I think you will find it difficult to adhere to Article 392 and use a cable
tray on a rooftop with source circuit conductors, if that is your hope.
-Glenn
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Chris Mason
Sent: Friday, March 22, 2013 3:08 PM
To: RE-wrenches
Subject: [RE-wrenches] Cable tray
I'm looking for flat roof cable tray system that is cost effective. We
previously used Cablofil and Cablo-port FSL 12" tray but it is very
expensive for our current application due to the size of the roof. We need
to install about 200' of tray and Cablofil galvanized is eating up the
budget. Can anyone recommend a cheaper alternative.
--
Chris Mason
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
--
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130325/453dc5b0/attachment-0004.html>
More information about the RE-wrenches
mailing list