[RE-wrenches] Micro inverters not on the roof.
Larry Crutcher, Starlight Solar Power Systems
larry at starlightsolar.com
Tue Dec 17 14:08:39 PST 2013
William,
If your Vmp drop is under 2% (my design goal for maximum acceptable loss) I can't see any reason why not.
Larry
On Dec 17, 2013, at 3:00 PM, "William Miller" <william at millersolar.com> wrote:
Friends:
I am reworking an existing off-grid system to become a grid-tie with micro-inverters. With your help, we have already determined that the M-190 inverters will work and we have acquired the 9 of them we need.
Since the installation was completed in 1996, the home owner has installed a shade cover over a skylight. Some of the supporting structure is preventing us from getting under the modules to install the M-190s. Each module was fed to the equipment cabinet since the combiner was located there. I have decided it will be much easier to install the M-190s in the equipment cabinet. We have everything we need there: The individual PV leads (in 10AWG), the breaker panel and room to mount the inverters. Can any of you see any reason why the M-190s can’t be installed no on the roof?
Thanks in advance,
William
<image002.jpg>
17395 Oak Rd. Atascadero, CA 93422
www.millersolar.com
805-438-5600 voice
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131217/bbd48b1a/attachment-0003.html>
More information about the RE-wrenches
mailing list