Hi Drake

The first thing I would look at is how the batteries are being charged... Can they even be charged by the present equipment? What is the Bulk/Absorb voltage and time? Equally important is the design of the bank... series or series/parallel and if parallel how many strings. Lastly which Trojan L-16 are these?

Tom Duffy
Senior Solar Design Engineer
[Real-logo-X-195]
Toll Free 888-895-8179
tom at thesolar.biz<mailto:tom at thesolar.biz>
Customer Service and Accounting 888-895-6810
Grid tie sales 888-895-7847
Off Grid sales 888-895-4058
Other Product Sales 888-895-9612
Central America Sales (Panama) 507-6-126-1253
Shipping and Receiving 888-895-6497
Tech Support 888-895-8179
SKYPE:  thesolarbiz

From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Drake
Sent: Monday, July 15, 2013 8:59 PM
To: RE-wrenches
Subject: [RE-wrenches] Trojan L-16s

Hello Wrenches,

A 1 1/2 year old bank of Trojan L-16s had a battery with a dead cell. I have heard that there have been some complaints about the L-16s lately.  Has anyone had experiences with Trojan L-16s (or the RE series), good or bad?  Are they still a good choice to use in off grid systems?

Thanks,

Drake

Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV
740-448-7328
http://athens-electric.com/

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130716/2cd6e537/attachment-0003.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 17364 bytes
Desc: image002.png
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130716/2cd6e537/attachment-0006.png>


More information about the RE-wrenches mailing list